GE Multilin
F60 Feeder Protection System
5-27
5 SETTINGS
5.2 PRODUCT SETUP
5
5.2.4 COMMUNICATIONS
a) MAIN MENU
PATH: SETTINGS
PRODUCT SETUP
COMMUNICATIONS
b) SERIAL PORTS
PATH: SETTINGS
PRODUCT SETUP
COMMUNICATIONS
SERIAL PORTS
RS485 COM2 BAUD RATE
and
PARITY
: The F60 is equipped with two independent serial communication ports. The faceplate
RS232 port is intended for local use and is fixed at 19200 bit/s baud and even parity. The rear COM2 port is RS485 and has
settings for baud rate and parity. It is important that these parameters agree with the settings used on the computer or other
equipment that is connected to these ports. Any of these ports can be connected to a computer running EnerVista UR
Setup. This software can download and upload setting files, view measured parameters, and upgrade the relay firmware. A
maximum of 32 relays can be daisy-chained and connected to a DCS, PLC, or computer using the RS485 ports. If IEC
60870-103 is chosen as the protocol, valid baud rates are 9600 and 19200 bit/s, and valid parity is Even.
COMMUNICATIONS
SERIAL PORTS
MESSAGE
NETWORK
MESSAGE
ROUTING
MESSAGE
MODBUS PROTOCOL
MESSAGE
PROTOCOL:
DNP 3.0
Range: DNP 3.0, IEC 60870-5-104, IEC 60870-5-103
MESSAGE
DNP PROTOCOL
MESSAGE
DNP / IEC104
POINT LISTS
MESSAGE
IEC 61850 PROTOCOL
MESSAGE
WEB SERVER
HTTP PROTOCOL
MESSAGE
TFTP PROTOCOL
MESSAGE
IEC 60870-5-104
PROTOCOL
MESSAGE
EGD PROTOCOL
MESSAGE
IEC103
PROTOCOL
SERIAL PORTS
RS485 COM2 BAUD RATE:
19200
Range: 300, 1200, 2400, 4800, 9600, 14400, 19200,
28800, 33600, 38400, 57600, 115200 bit/s
MESSAGE
RS485 COM2 PARITY:
Even
Range: None, Odd, Even
MESSAGE
RS485 COM2 RESPONSE
MIN TIME:
0 ms
Range: 0 to 1000 ms in steps of 10
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...