F60 Feeder Protection System
5-105
5 SETTINGS
5.4 SYSTEM SETUP
5
Figure 5–25: DISTURBANCE DETECTOR LOGIC DIAGRAM
The disturbance detector responds to the change in currents of twice the current cut-off level. The default cut-off threshold
is 0.02 pu; thus by default the disturbance detector responds to a change of 0.04 pu. The metering sensitivity setting (
PROD-
UCT SETUP
DISPLAY PROPERTIES
CURRENT CUT-OFF LEVEL
) controls the sensitivity of the disturbance detector
accordingly.
EXAMPLE USE OF SOURCES:
An example of the use of sources is shown in the diagram below. A relay could have the following hardware configuration:
This configuration could be used on a two-winding transformer, with one winding connected into a breaker-and-a-half sys-
tem. The following figure shows the arrangement of sources used to provide the functions required in this application, and
the CT/VT inputs that are used to provide the data.
827092A3.CDR
SOURCE 1
CURRENT PHASOR
PRODUCT SETUP/DISPLAY
PROPERTIES/CURRENT
CUT-OFF LEVEL
PRODUCT SETUP/DISPLAY
PROPERTIES/CURRENT
CUT-OFF LEVEL
PRODUCT SETUP/DISPLAY
PROPERTIES/CURRENT
CUT-OFF LEVEL
SOURCE 2
CURRENT PHASOR
SOURCE 6
CURRENT PHASOR
ACTUAL
SETTING
SETTING
SETTING
ACTUAL
ACTUAL
FLEXLOGIC OPERAND
FLEXLOGIC OPERAND
FLEXLOGIC OPERAND
I
_1
I
_1
I
_1
SRC 1 50DD OP
SRC 2 50DD OP
SRC 6 50DD OP
I
_2
I
_2
I
_2
I
_0
I
_0
I
_0
OR
OR
OR
Where ’ is 2 cycles old
I
Where ’ is 2 cycles old
I
Where ’ is 2 cycles old
I
I
I
_1 - _1’ >2*CUT-OFF
I
I
_1 - _1’ >2*CUT-OFF
I
I
_1 - _1’ >2*CUT-OFF
I
I
_2 - _2’ >2*CUT-OFF
I
I
_2 - _2’ >2*CUT-OFF
I
I
_2 - _2’ >2*CUT-OFF
I
I
_0 - _0’ >2*CUT-OFF
I
I
_0 - _0’ >2*CUT-OFF
I
I
_0 - _0’ >2*CUT-OFF
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...