5-202
F60 Feeder Protection System
GE Multilin
5.6 GROUPED ELEMENTS
5 SETTINGS
5
b) NEGATIVE SEQUENCE TIME OVERCURRENT
(ANSI 51Q, IEC PTOC)
PATH: SETTINGS
GROUPED ELEMENTS
SETTING GROUP 1(6)
NEGATIVE SEQUENCE CURRENT
NEG SEQ TOC1(2)
The negative-sequence time overcurrent element may be used to determine and clear unbalance in the system. The input
for calculating negative-sequence current is the fundamental phasor value.
Two methods of resetting operation are available; “Timed” and “Instantaneous” (refer to the
Inverse Time Overcurrent Char-
acteristics
sub-section for details on curve setup, trip times and reset operation). When the element is blocked, the time
accumulator resets according to the reset characteristic. For example, if the element reset characteristic is set to “Instanta-
neous” and the element is blocked, the time accumulator is cleared immediately.
Figure 5–85: NEGATIVE SEQUENCE TOC1 SCHEME LOGIC
NEG SEQ TOC1
NEG SEQ TOC1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
NEG SEQ TOC1 SIGNAL
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
NEG SEQ TOC1
PICKUP: 1.000 pu
Range: 0.000 to 30.000 pu in steps of 0.001
MESSAGE
NEG SEQ TOC1
CURVE: IEEE Mod Inv
Range: see OVERCURRENT CURVE TYPES table
MESSAGE
NEG SEQ TOC1
TD MULTIPLIER: 1.00
Range: 0.00 to 600.00 in steps of 0.01
MESSAGE
NEG SEQ TOC1
RESET: Instantaneous
Range: Instantaneous, Timed
MESSAGE
NEG SEQ TOC1 BLOCK:
Off
Range: FlexLogic operand
MESSAGE
NEG SEQ TOC1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
NEG SEQ TOC1
EVENTS: Disabled
Range: Disabled, Enabled
FLEXLOGIC OPERANDS
NEG SEQ TOC1 FUNCTION:
NEG SEQ TOC1 PICKUP:
NEG SEQ TOC1 CURVE:
NEG SEQ TOC1 TD MULTIPLIER:
NEG SEQ TOC1 RESET:
NEG SEQ TOC1 INPUT:
NEG SEQ TOC1 SOURCE:
NEG SEQ TOC1 BLOCK:
NEG SEQ TOC1 DPO
NEG SEQ TOC1 OP
NEG SEQ TOC1 PKP
AND
827057A5.CDR
SETTING
SETTING
Enabled=1
SETTING
SETTING
Neg Seq
Off=0
t
NEG SEQ
PICKUP
<
RUN
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...