5 SETTINGS
5.6 GROUPED ELEMENTS
5
•
DIR POWER 1 RCA:
Specifies the relay characteristic angle (RCA) for the sensitive directional power function. Appli-
cation of this setting is threefold:
1.
It allows the element to respond to active or reactive power in any direction (active overpower/underpower, etc.).
2.
Together with a precise calibration angle, it allows compensation for any CT and VT angular errors to permit more
sensitive settings.
3.
It allows for required direction in situations when the voltage signal is taken from behind a delta-wye connected
power transformer and the phase angle compensation is required.
For example, the active overpower characteristic is achieved by setting
DIR POWER 1 RCA
to “0°”, reactive overpower by
setting
DIR POWER 1 RCA
to “90°”, active underpower by setting
DIR POWER 1 RCA
to “180°”, and reactive underpower by
setting
DIR POWER 1 RCA
to “270°”.
•
DIR POWER 1 CALIBRATION:
This setting allows the relay characteristic angle to change in steps of 0.05°. This may
be useful when a small difference in VT and CT angular errors is to be compensated to permit more sensitive settings.
This setting virtually enables calibration of the directional power function in terms of the angular error of applied VTs
and CTs. The element responds to the sum of the
DIR POWER 1 RCA
and
DIR POWER 1 CALIBRATION
settings.
•
DIR POWER 1 STG1 SMIN:
This setting specifies the minimum power as defined along the relay characteristic angle
(RCA) for the stage 1 of the element. The positive values imply a shift towards the operate region along the RCA line;
the negative values imply a shift towards the restrain region along the RCA line. Refer to the
Directional power sample
applications
figure for details. Together with the RCA, this setting enables a wide range of operating characteristics.
This setting applies to three-phase power and is entered in per-unit (pu) values. The base quantity is 3 x VT pu base x
CT pu base.
For example, a setting of 2% for a 200 MW machine is 0.02
×
200 MW = 4 MW. If 13.8kV is line voltage and 10 kA is a
primary CT current, the source pu quantity is 239 MVA, and thus, SMIN should be set at 4 MW / 239 MVA = 0.0167 pu
≈
0.017 pu. If the reverse power application is considered, RCA = 180° and SMIN = 0.017 pu.
The element drops out if the magnitude of the positive-sequence current becomes virtually zero, that is, it drops below
the cutoff level.
•
DIR POWER 1 STG1 DELAY:
This setting specifies a time delay for stage 1. For reverse power or low forward power
applications for a synchronous machine, stage 1 is typically applied for alarming and stage 2 for tripping.
Figure 5–104: SENSITIVE DIRECTIONAL POWER SCHEME LOGIC
842003A3.CDR
DIR POWER 1 BLK:
SETTING
Off = 0
DIRECTIONAL POWER
CHARACTERISTICS
RUN
FLEXLOGIC OPERANDS
DIR POWER 1 SOURCE:
SETTING
Three-phase active power (P)
Three-phase reactive power (Q)
DIR POWER 1 STG1
SMIN:
DIR POWER 1
CALIBRATION:
SETTING
DIR POWER 1 STG1
DELAY:
t
PKP
100 ms
DIR POWER 1
FUNCTION:
SETTING
Enabled = 1
SETTING
DIR POWER 1 STG2
DELAY:
DIR POWER 1 STG1 OP
DIR POWER 1 STG2 PKP
DIR POWER 1 STG2 DPO
DIR POWER 1 STG2 OP
DIR POWER 1 PKP
DIR POWER 1 DPO
DIR POWER 1 OP
FLEXLOGIC™ OPERANDS
DIR POWER 1 STG1 PKP
DIR POWER 1 STG1 DPO
100 ms
OR
SETTINGS
DIR POWER 1 RCA:
OR
t
PKP
DIR POWER 1 STG2
SMIN:
AND
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...