5-244
F60 Feeder Protection System
GE Multilin
5.7 CONTROL ELEMENTS
5 SETTINGS
5
The voltages V1 and V2 will be matched automatically so that the corresponding voltages from the two sources will be
used to measure conditions. A phase to phase voltage will be used if available in both sources; if one or both of the
Sources have only an auxiliary voltage, this voltage will be used. For example, if an auxiliary voltage is programmed to
VAG, the synchrocheck element will automatically select VAG from the other source. If the comparison is required on a
specific voltage, the user can externally connect that specific voltage to auxiliary voltage terminals and then use this
"Auxiliary Voltage" to check the synchronism conditions.
If using a single CT/VT module with both phase voltages and an auxiliary voltage, ensure that only the auxiliary voltage
is programmed in one of the sources to be used for synchrocheck.
Exception: Synchronism cannot be checked between Delta connected phase VTs and a Wye connected auxil-
iary voltage.
2.
The relay measures frequency and Volts/Hz from an input on a given source with priorities as established by the con-
figuration of input channels to the source. The relay will use the phase channel of a three-phase set of voltages if pro-
grammed as part of that source. The relay will use the auxiliary voltage channel only if that channel is programmed as
part of the Source and a three-phase set is not.
4
Phase VT and
Auxiliary VT
Auxiliary VT
Phase
Auxiliary
V auxiliary
(as set for Source z)
5
Auxiliary VT
Auxiliary VT
Auxiliary
Auxiliary
V auxiliary
(as set for selected sources)
NO.
V1 OR V2
(SOURCE Y)
V2 OR V1
(SOURCE Z)
AUTO-SELECTED
COMBINATION
AUTO-SELECTED VOLTAGE
SOURCE Y
SOURCE Z
NOTE
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...