i) THERMAL OVERLOAD PROTECTION
(ANSI 49)
PATH: SETTINGS
CONTROL ELEMENTS
MONITORING ELEMENTS
THERMAL OVERLOAD PROTECTION
THERMAL
PROTECTION 1(2)
The thermal overload protection element corresponds to the IEC 255-8 standard and is used to detect thermal overload
conditions in protected power system elements. Choosing an appropriate time constant element can be used to protect dif-
ferent elements of the power system. The cold curve characteristic is applied when the estimated
I
p
current is less than
10% of the base current. If
I
p
current is greater or equal than 10% than the base current, then the hot curve characteristic is
applied.
I
p
current is estimated with a fixed time constant for both cooling and heating that reaches to the final value in two
seconds on a step change (either step up or step down) signal.
The IEC255-8 cold curve is defined as follows:
(EQ 5.32)
The IEC255-8 hot curve is defined as follows:
(EQ 5.33)
In the above equations,
•
t
op
= time to operate
•
τ
op
= thermal protection trip time constant
•
I
= measured overload RMS current
•
I
p
= measured load RMS current before overload occurs
•
k
= IEC 255-8 k-factor applied to
I
B
, defining maximum permissible current above nominal current
THERMAL
PROTECTION 1
THERMAL PROTECTION 1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
THERMAL PROTECTION 1
SOURCE: SRC1
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
THERMAL PROTECTION 1
BASE CURR: 0.80 pu
Range: 0.20 to 3.00 pu in steps of 0.01
MESSAGE
THERMAL PROTECTION 1
k FACTOR: 1.10
Range: 1.00 to 1.20 in steps of 0.05
MESSAGE
THERM PROT 1 TRIP
TIME CONST: 45 min.
Range: 0 to 1000 min. in steps of 1
MESSAGE
THERM PROT 1 RESET
TIME CONST: 45 min.
Range: 0 to 1000 min. in steps of 1
MESSAGE
THERM PROT 1 MINIM
RESET TIME: 20 min.
Range: 0 to 1000 min. in steps of 1
MESSAGE
THERM PROT 1 RESET:
Off
Range: FlexLogic operand
MESSAGE
THERM PROT 1 BLOCK:
Off
Range: FlexLogic operand
MESSAGE
THERMAL PROTECTION 1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
THERMAL PROTECTION 1
EVENTS: Disabled
Range: Disabled, Enabled
t
op
τ
op
I
2
I
2
kI
B
(
)
2
–
--------------------------
ln
×
=
t
op
τ
op
I
2
I
p
2
–
I
2
kI
B
(
)
2
–
--------------------------
ln
×
=
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...