B-48
F60 Feeder Protection System
GE Multilin
B.4 MEMORY MAPPING
APPENDIX B
B
7DD0
...Repeated for User Programmable Pushbutton 14
7E00
...Repeated for User Programmable Pushbutton 15
7E30
...Repeated for User Programmable Pushbutton 16
High Impedance Fault Detection (Hi-Z) Settings (Read/Write Setting)
7E60
Hi-Z Function
0 to 1
---
1
F102
0 (Disabled)
7E61
Hi-Z Signal Source
0 to 5
---
1
F167
0 (SRC 1)
7E62
Hi-Z Arcing Sensitivity
1 to 10
---
1
F001
5
7E63
Hi-Z Phase Event Count
10 to 250
---
1
F001
30
7E64
Hi-Z Ground Event Count
10 to 500
---
1
F001
30
7E65
Hi-Z Event Count Time
5 to 180
min
1
F001
15
7E66
Hi-Z Overcurrent Protection Coordination Timeout
10 to 200
s
1
F001
15
7E67
Hi-Z Phase Overcurrent Minimum Pickup
0.01 to 10
pu
0.01
F001
150
7E68
Hi-Z Neutral Overcurrent Minimum Pickup
0.01 to 10
pu
0.01
F001
100
7E69
Hi-Z Phase Rate of Change
1 to 999
A/2cycle
1
F001
150
7E6A
Hi-Z Neutral Rate of Change
1 to 999
A/2cycle
1
F001
150
7E6B
Hi-Z Loss of Load Threshold
5 to 100
%
1
F001
15
7E6C
Hi-Z 3-Phase Event Threshold
1 to 1000
A
1
F001
25
7E6D
Hi-Z Voltage Supervision Threshold
0 to 100
%
1
F001
5
7E6E
Hi-Z Voltage Supervision Delay
0 to 3000
cycles
2
F001
60
7E6F
HIZ Even Harmonic Restraint
0 to 100
%
1
F001
20
7E70
Hi-Z Target
0 to 2
---
1
F109
0 (Self-reset)
7E71
Hi-Z Events
0 to 1
---
1
F102
0 (Disabled)
7E72
Hi-Z Arcing Reset Time
0 to 6000
s
0.1
F001
0
Neutral Overvoltage (Read/Write Grouped Setting) (3 modules)
7F00
Neutral Overvoltage 1 Function
0 to 1
---
1
F102
0 (Disabled)
7F01
Neutral Overvoltage 1 Signal Source
0 to 5
---
1
F167
0 (SRC 1)
7F02
Neutral Overvoltage 1 Pickup
0 to 3
pu
0.001
F001
300
7F03
Neutral Overvoltage 1 Pickup Delay
0 to 600
s
0.01
F001
100
7F04
Neutral Overvoltage 1 Reset Delay
0 to 600
s
0.01
F001
100
7F05
Neutral Overvoltage 1 Block
0 to 4294967295
---
1
F300
0
7F07
Neutral Overvoltage 1 Target
0 to 2
---
1
F109
0 (Self-reset)
7F08
Neutral Overvoltage 1 Events
0 to 1
---
1
F102
0 (Disabled)
7F09
Neutral Overvoltage 1 Curves
0 to 3
---
1
F116
0 (Definite Time)
7F0A
Reserved (7 items)
0 to 65535
---
1
F001
0
7F11
...Repeated for Neutral Overvoltage 2
7F22
...Repeated for Neutral Overvoltage 3
Auxiliary Undervoltage (Read/Write Grouped Setting (2 modules)
7F60
Auxiliary Undervoltage 1 Function
0 to 1
---
1
F102
0 (Disabled)
7F61
Auxiliary Undervoltage 1 Signal Source
0 to 5
---
1
F167
0 (SRC 1)
7F62
Auxiliary Undervoltage 1 Pickup
0 to 3
pu
0.001
F001
700
7F63
Auxiliary Undervoltage 1 Delay
0 to 600
s
0.01
F001
100
7F64
Auxiliary Undervoltage 1 Curve
0 to 1
---
1
F111
0 (Definite Time)
7F65
Auxiliary Undervoltage 1 Minimum Voltage
0 to 3
pu
0.001
F001
100
7F66
Auxiliary Undervoltage 1 Block
0 to 4294967295
---
1
F300
0
7F68
Auxiliary Undervoltage 1 Target
0 to 2
---
1
F109
0 (Self-reset)
7F69
Auxiliary Undervoltage 1 Events
0 to 1
---
1
F102
0 (Disabled)
7F6A
Reserved (7 items)
0 to 65535
---
1
F001
0
7F71
...Repeated for Auxiliary Undervoltage 2
Auxiliary Overvoltage (Read/Write Grouped Setting) (2 modules)
7FA0
Auxiliary Overvoltage 1 Function
0 to 1
---
1
F102
0 (Disabled)
7FA1
Auxiliary Overvoltage 1 Signal Source
0 to 5
---
1
F167
0 (SRC 1)
7FA2
Auxiliary Overvoltage 1 Pickup
0 to 3
pu
0.001
F001
300
7FA3
Auxiliary Overvoltage 1 Pickup Delay
0 to 600
s
0.01
F001
100
7FA4
Auxiliary Overvoltage 1 Reset Delay
0 to 600
s
0.01
F001
100
Table B–10: MODBUS MEMORY MAP (Sheet 40 of 70)
ADDR
REGISTER NAME
RANGE
UNITS
STEP
FORMAT
DEFAULT
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...