B-94
F60 Feeder Protection System
GE Multilin
B.4 MEMORY MAPPING
APPENDIX B
B
[10] CONTACT OUTPUTS VOLTAGE DETECTED (1 to 64)
[11] CONTACT OUTPUTS VOLTAGE OFF DETECTED (1 to 64)
[12] CONTACT OUTPUTS CURRENT DETECTED (1 to 64)
[13] CONTACT OUTPUTS CURRENT OFF DETECTED (1 to 64)
[14] REMOTE INPUTS (1 to 32)
[16] DIRECT INPUTS (1 to 96
[18] REMOTE OUTPUT DNA BIT PAIRS (1 to 32)
[20] REMOTE OUTPUT UserSt BIT PAIRS (1 to 32)
[22] REMOTE DEVICE ONLINE (1 to 16)
[24] MISCELLANEOUS EQUATION
[26] TELEPROTECTION INPUTS
[28] INSERT (via keypad only)
[30] DELETE (via keypad only)
[32] END
[34] NOT (1 INPUT)
[36] 2 INPUT XOR (0)
[38] LATCH SET/RESET (2 inputs)
[40] OR (2 to 16 inputs)
[42] AND (2 to 16 inputs)
[44] NOR (2 to 16 inputs)
[46] NAND (2 to 16 inputs)
[48] TIMER (1 to 32)
[50] ASSIGN VIRTUAL OUTPUT (1 to 64)
[52] ONE SHOT
[54] SELF-TEST ERROR (see F141 for range)
[56] PLATFORM DIRECT INPUT (1 to 96)
[58] PLATFORM DIRECT OUTPUT (1 to 96)
[60] PLATFORM DIRECT DEVICE (1 to 8)
[62] MISCELLANEOUS EVENTS (see F146 for range)
[64] PDC NETWORK CONTROL
[66] PMU RECORDER OUT OF MEMORY
[68] PMU RECORDER STOPPED
[128 to 255] ELEMENT STATES (see the Element States section
in the Modbus memory map)
F400
UR_UINT16: CT/VT BANK SELECTION
F491
ENUMERATION: ANALOG INPUT MODE
0 = Default Value, 1 = Last Known
F500
UR_UINT16: PACKED BITFIELD
First register indicates input/output state with bits 0 (MSB) to 15
(LSB) corresponding to input/output state 1 to 16. The second reg-
ister indicates input/output state with bits 0 to 15 corresponding to
input/output state 17 to 32 (if required). The third register indicates
input/output state with bits 0 to 15 corresponding to input/output
state 33 to 48 (if required). The fourth register indicates input/out-
put state with bits 0 to 15 corresponding to input/output state 49 to
64 (if required).
The number of registers required is determined by the specific
data item. A bit value of 0 = Off and 1 = On.
F501
UR_UINT16: LED STATUS
Low byte of register indicates LED status with bit 0 representing
the top LED and bit 7 the bottom LED. A bit value of 1 indicates
the LED is on, 0 indicates the LED is off.
0 = Off, 1 = On
F502
BITFIELD: ELEMENT OPERATE STATES
Each bit contains the operate state for an element. See the F124
format code for a list of element IDs. The operate bit for element ID
X is bit [X mod 16] in register [X/16].
F515
ENUMERATION ELEMENT INPUT MODE
0 = Signed, 1 = Absolute
F516
ENUMERATION ELEMENT COMPARE MODE
0 = Level, 1 = Delta
F517
ENUMERATION: ELEMENT DIRECTION OPERATION
0 = Over, 1 = Under
F518
ENUMERATION: FLEXELEMENT UNITS
0 = Milliseconds, 1 = Seconds, 2 = Minutes
F519
ENUMERATION: NON-VOLATILE LATCH
0 = Reset-Dominant, 1 = Set-Dominant
F522
ENUMERATION: TRANSDUCER DCmA OUTPUT RANGE
0 = –1 to 1 mA, 1 = 0 to 1 mA, 2 = 4 to 20 mA
F523
ENUMERATION: DNP OBJECTS 20, 22, AND 23 DEFAULT
VARIATION
Bitmask
Bank selection
0
Card 1 Contact 1 to 4
1
Card 1 Contact 5 to 8
2
Card 2 Contact 1 to 4
3
Card 2 Contact 5 to 8
4
Card 3 Contact 1 to 4
5
Card 3 Contact 5 to 8
Bitmask
Default variation
0
1
1
2
2
5
3
6
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...