C-4
F60 Feeder Protection System
GE Multilin
C.2 SERVER DATA ORGANIZATION
APPENDIX C
C
C.2.6 MMXU: ANALOG MEASURED VALUES
A limited number of measured analog values are available through the MMXU logical nodes.
Each MMXU logical node provides data from a F60 current and voltage source. There is one MMXU available for each con-
figurable source (programmed in the
SETTINGS
SYSTEM SETUP
SIGNAL SOURCES
menu). MMXU1 provides data
from F60 source 1, and MMXU2 provides data from F60 source 2.
MMXU data is provided in two forms: instantaneous and deadband. The instantaneous values are updated every time a
read operation is performed by a client. The deadband values are calculated as described in IEC 61850 parts 7-1 and 7-3.
The selection of appropriate deadband settings for the F60 is described in chapter 5 of this manual.
IEC 61850 buffered and unbuffered reporting capability is available in all MMXU logical nodes. MMXUx logical nodes pro-
vide the following data for each source:
•
MMXU1.MX.TotW: three-phase real power
•
MMXU1.MX.TotVAr: three-phase reactive power
•
MMXU1.MX.TotVA: three-phase apparent power
•
MMXU1.MX.TotPF: three-phase power factor
•
MMXU1.MX.Hz: frequency
•
MMXU1.MX.PPV.phsAB: phase AB voltage magnitude and angle
•
MMXU1.MX.PPV.phsBC: phase BC voltage magnitude and angle
•
MMXU1.MX.PPV.phsCA: Phase CA voltage magnitude and angle
•
MMXU1.MX.PhV.phsA: phase AG voltage magnitude and angle
•
MMXU1.MX.PhV.phsB: phase BG voltage magnitude and angle
•
MMXU1.MX.PhV.phsC: phase CG voltage magnitude and angle
•
MMXU1.MX.A.phsA: phase A current magnitude and angle
•
MMXU1.MX.A.phsB: phase B current magnitude and angle
•
MMXU1.MX.A.phsC: phase C current magnitude and angle
•
MMXU1.MX.A.neut: ground current magnitude and angle
•
MMXU1.MX.W.phsA: phase A real power
•
MMXU1.MX.W.phsB: phase B real power
•
MMXU1.MX.W.phsC: phase C real power
•
MMXU1.MX.VAr.phsA: phase A reactive power
•
MMXU1.MX.VAr.phsB: phase B reactive power
•
MMXU1.MX.VAr.phsC: phase C reactive power
•
MMXU1.MX.VA.phsA: phase A apparent power
•
MMXU1.MX.VA.phsB: phase B apparent power
•
MMXU1.MX.VA.phsC: phase C apparent power
•
MMXU1.MX.PF.phsA: phase A power factor
•
MMXU1.MX.PF.phsB: phase B power factor
•
MMXU1.MX.PF.phsC: phase C power factor
C.2.7 PROTECTION AND OTHER LOGICAL NODES
The following list describes the protection elements for all UR-series relays. The F60 relay will contain a subset of protec-
tion elements from this list.
•
PDIF: bus differential, transformer instantaneous differential, transformer percent differential, current differential
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...