GE Multilin
F60 Feeder Protection System
5-37
5 SETTINGS
5.2 PRODUCT SETUP
5
j) DNP PROTOCOL
PATH: SETTINGS
PRODUCT SETUP
COMMUNICATIONS
DNP PROTOCOL
DNP PROTOCOL
DNP CHANNELS
Range: see sub-menu below
MESSAGE
DNP ADDRESS:
1
Range: 0 to 65519 in steps of 1
MESSAGE
DNP NETWORK
CLIENT ADDRESSES
Range: see sub-menu below
MESSAGE
DNP TCP/UDP PORT
NUMBER: 20000
Range: 0 to 65535 in steps of 1
MESSAGE
DNP UNSOL RESPONSE
FUNCTION: Disabled
Range: Enabled, Disabled
MESSAGE
DNP UNSOL RESPONSE
TIMEOUT: 5 s
Range: 0 to 60 s in steps of 1
MESSAGE
DNP UNSOL RESPONSE
MAX RETRIES: 10
Range: 1 to 255 in steps of 1
MESSAGE
DNP UNSOL RESPONSE
DEST ADDRESS: 1
Range: 0 to 65519 in steps of 1
MESSAGE
DNP CURRENT SCALE
FACTOR: 1
Range: 0.001, 0.01. 0.1, 1, 10, 100, 1000, 10000,
100000
MESSAGE
DNP VOLTAGE SCALE
FACTOR: 1
Range: 0.001, 0.01. 0.1, 1, 10, 100, 1000, 10000,
100000
MESSAGE
DNP POWER SCALE
FACTOR: 1
Range: 0.001, 0.01. 0.1, 1, 10, 100, 1000, 10000,
100000
MESSAGE
DNP ENERGY SCALE
FACTOR: 1
Range: 0.001, 0.01. 0.1, 1, 10, 100, 1000, 10000,
100000
MESSAGE
DNP PF SCALE
FACTOR: 1
Range: 0.001, 0.01. 0.1, 1, 10, 100, 1000, 10000,
100000
MESSAGE
DNP OTHER SCALE
FACTOR: 1
Range: 0.001, 0.01. 0.1, 1, 10, 100, 1000, 10000,
100000
MESSAGE
DNP CURRENT DEFAULT
DEADBAND: 30000
Range: 0 to 100000000 in steps of 1
MESSAGE
DNP VOLTAGE DEFAULT
DEADBAND: 30000
Range: 0 to 100000000 in steps of 1
MESSAGE
DNP POWER DEFAULT
DEADBAND: 30000
Range: 0 to 100000000 in steps of 1
MESSAGE
DNP ENERGY DEFAULT
DEADBAND: 30000
Range: 0 to 100000000 in steps of 1
MESSAGE
DNP PF DEFAULT
DEADBAND: 30000
Range: 0 to 100000000 in steps of 1
MESSAGE
DNP OTHER DEFAULT
DEADBAND: 30000
Range: 0 to 100000000 in steps of 1
MESSAGE
DNP TIME SYNC IIN
PERIOD: 1440 min
Range: 1 to 10080 min. in steps of 1
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...