5-58
F60 Feeder Protection System
GE Multilin
5.2 PRODUCT SETUP
5 SETTINGS
5
PATH: SETTINGS
PRODUCT SETUP
COMMUNICATIONS
IEC 60870-5-104 PROTOCOL
IEC NETWORK CLIENT
ADDRESSES
The F60 can specify a maximum of five clients for its IEC 104 connections. These are IP addresses for the controllers to
which the F60 can connect.
A maximum of two simultaneous connections are supported at any given time.
p) EGD PROTOCOL
PATH: SETTINGS
PRODUCT SETUP
COMMUNICATIONS
EGD PROTOCOL
The F60 Feeder Protection System is provided with optional Ethernet Global Data (EGD) communications
capability. This feature is specified as a software option at the time of ordering. See the
Order Codes
sec-
tion in chapter 2 for details.
The relay supports one fast Ethernet Global Data (EGD) exchange and two slow EGD exchanges. There are 20 data items
in the fast-produced EGD exchange and 50 data items in each slow-produced exchange.
Ethernet Global Data (EGD) is a suite of protocols used for the real-time transfer of data for display and control purposes.
The relay can be configured to ‘produce’ EGD data exchanges, and other devices can be configured to ‘consume’ EGD
data exchanges. The number of produced exchanges (up to three), the data items in each exchange (up to 50), and the
exchange production rate can be configured.
EGD cannot be used to transfer data between UR-series relays. The relay supports EGD production only. An EGD
exchange will not be transmitted unless the destination address is non-zero, and at least the first data item address is set to
a valid Modbus register address. Note that the default setting value of “0” is considered invalid.
IEC NETWORK
CLIENT ADDRESSES
CLIENT ADDRESS 1:
0.0.0.0
Range: Standard IPV4 address format
MESSAGE
CLIENT ADDRESS 2:
0.0.0.0
Range: Standard IPV4 address format
MESSAGE
CLIENT ADDRESS 3:
0.0.0.0
Range: Standard IPV4 address format
MESSAGE
CLIENT ADDRESS 4:
0.0.0.0
Range: Standard IPV4 address format
MESSAGE
CLIENT ADDRESS 5:
0.0.0.0
Range: Standard IPV4 address format
EGD PROTOCOL
FAST PROD EXCH 1
CONFIGURATION
MESSAGE
SLOW PROD EXCH 1
CONFIGURATION
MESSAGE
SLOW PROD EXCH 2
CONFIGURATION
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...