GE Multilin
F60 Feeder Protection System
5-79
5 SETTINGS
5.2 PRODUCT SETUP
5
APPLICATION EXAMPLE 2:
Assume one needs to check if any LEDs are “burned” as well as exercise one LED at a time to check for other failures. This
is to be performed via user-programmable pushbutton 1.
After applying the settings in application example 1, hold down the pushbutton as long as necessary to test all LEDs. Next,
release the pushbutton to automatically start stage 2. Once stage 2 has started, the pushbutton can be released. When
stage 2 is completed, stage 3 will automatically start. The test may be aborted at any time by pressing the pushbutton.
c) TRIP AND ALARM LEDS
PATH: SETTINGS
PRODUCT SETUP
USER-PROGRAMMABLE LEDS
TRIP & ALARM LEDS
The trip and alarm LEDs are in the first LED column (enhanced faceplate) and on LED panel 1 (standard faceplate). Each
indicator can be programmed to become illuminated when the selected FlexLogic operand is in the logic 1 state.
d) USER-PROGRAMMABLE LED 1(48)
PATH: SETTINGS
PRODUCT SETUP
USER-PROGRAMMABLE LEDS
USER-PROGRAMMABLE LED 1(48)
There are 48 amber LEDs across the relay faceplate LED panels. Each of these indicators can be programmed to illumi-
nate when the selected FlexLogic operand is in the logic 1 state.
For the standard faceplate, the LEDs are located as follows.
•
LED Panel 2: user-programmable LEDs 1 through 24
•
LED Panel 3: user programmable LEDs 25 through 48
For the enhanced faceplate, the LEDs are located as follows.
•
LED column 2: user-programmable LEDs 1 through 12
•
LED column 3: user-programmable LEDs 13 through 24
•
LED column 4: user-programmable LEDs 25 through 36
•
LED column 5: user-programmable LEDs 37 through 48
See the
LED Indicators
section in chapter 4 for information on the location of these indexed LEDs.
The user-programmable LED settings select the FlexLogic operands that control the LEDs. If the
LED 1 TYPE
setting is “Self-
Reset” (the default setting), the LED illumination will track the state of the selected LED operand. If the
LED 1 TYPE
setting is
“Latched”, the LED, once lit, remains so until reset by the faceplate RESET button, from a remote device via a communica-
tions channel, or from any programmed operand, even if the LED operand state de-asserts.
TRIP & ALARM LEDS
TRIP LED INPUT:
Off
Range: FlexLogic operand
MESSAGE
ALARM LED INPUT:
Off
Range: FlexLogic operand
USER-PROGRAMMABLE
LED 1
LED 1 OPERAND:
Off
Range: FlexLogic operand
MESSAGE
LED 1 TYPE:
Self-Reset
Range: Self-Reset, Latched
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...