1.5.7 COMMISSIONING
The F60 requires minimal maintenance after it is commissioned into service. Since the F60 is a microprocessor-based
relay, its characteristics do not change over time. As such, no further functional tests are required. Expected service life is
20 years for UR devices manufactured June 2014 or later when applied in a controlled indoors environment and electrical
conditions within specification.
The F60 performs a number of continual self-tests and takes the necessary action in case of any major errors (see the
Relay Self-tests
section in chapter 7). However, it is recommended that F60 maintenance be scheduled with other system
maintenance. This maintenance can involve in-service, out-of-service, or unscheduled maintenance.
In-service maintenance:
1.
Visual verification of the analog values integrity, such as voltage and current (in comparison to other devices on the
corresponding system).
2.
Visual verification of active alarms, relay display messages, and LED indications.
3.
LED test.
4.
Visual inspection for any damage, corrosion, dust, or loose wires.
5.
Event recorder file download with further events analysis.
Out-of-service maintenance:
1.
Check wiring connections for firmness.
2.
Analog values (currents, voltages, RTDs, analog inputs) injection test and metering accuracy verification. Calibrated
test equipment is required.
3.
Protection elements setting verification (analog values injection or visual verification of setting file entries against relay
settings schedule).
4.
Contact inputs and outputs verification. This test can be conducted by direct change of state forcing or as part of the
system functional testing.
5.
Visual inspection for any damage, corrosion, or dust.
6.
Event recorder file download with further events analysis.
7.
LED Test and pushbutton continuity check.
Unscheduled maintenance, such as a disturbance causing system interruption:
1.
View the event recorder and oscillography or fault report for correct operation of inputs, outputs, and elements.
If it is concluded that the relay or one of its modules is of concern, contact GE Multilin for service.
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...