5-174
F60 Feeder Protection System
GE Multilin
5.6 GROUPED ELEMENTS
5 SETTINGS
5
IAC CURVES:
The curves for the General Electric type IAC relay family are derived from the formulae:
,
(EQ 5.10)
where:
T
= operate time (in seconds),
TDM
= Multiplier setting,
I
= Input current,
I
pkp
= Pickup Current setting,
A to
E
=
constants,
t
r
= characteristic constant, and
T
RESET
= reset time in seconds (assuming energy capacity is 100%
and
RESET
is “Timed”)
Table 5–27: GE TYPE IAC INVERSE TIME CURVE CONSTANTS
IAC CURVE SHAPE
A
B
C
D
E
T
R
IAC Extreme Inverse
0.0040
0.6379
0.6200
1.7872
0.2461
6.008
IAC Very Inverse
0.0900
0.7955
0.1000
–1.2885
7.9586
4.678
IAC Inverse
0.2078
0.8630
0.8000
–0.4180
0.1947
0.990
IAC Short Inverse
0.0428
0.0609
0.6200
–0.0010
0.0221
0.222
Table 5–28: IAC CURVE TRIP TIMES
MULTIPLIER
(TDM)
CURRENT (
I
/
I
pickup
)
1.5
2.0
3.0
4.0
5.0
6.0
7.0
8.0
9.0
10.0
IAC EXTREMELY INVERSE
0.5
1.699
0.749
0.303
0.178
0.123
0.093
0.074
0.062
0.053
0.046
1.0
3.398
1.498
0.606
0.356
0.246
0.186
0.149
0.124
0.106
0.093
2.0
6.796
2.997
1.212
0.711
0.491
0.372
0.298
0.248
0.212
0.185
4.0
13.591
5.993
2.423
1.422
0.983
0.744
0.595
0.495
0.424
0.370
6.0
20.387
8.990
3.635
2.133
1.474
1.115
0.893
0.743
0.636
0.556
8.0
27.183
11.987
4.846
2.844
1.966
1.487
1.191
0.991
0.848
0.741
10.0
33.979
14.983
6.058
3.555
2.457
1.859
1.488
1.239
1.060
0.926
IAC VERY INVERSE
0.5
1.451
0.656
0.269
0.172
0.133
0.113
0.101
0.093
0.087
0.083
1.0
2.901
1.312
0.537
0.343
0.266
0.227
0.202
0.186
0.174
0.165
2.0
5.802
2.624
1.075
0.687
0.533
0.453
0.405
0.372
0.349
0.331
4.0
11.605
5.248
2.150
1.374
1.065
0.906
0.810
0.745
0.698
0.662
6.0
17.407
7.872
3.225
2.061
1.598
1.359
1.215
1.117
1.046
0.992
8.0
23.209
10.497
4.299
2.747
2.131
1.813
1.620
1.490
1.395
1.323
10.0
29.012
13.121
5.374
3.434
2.663
2.266
2.025
1.862
1.744
1.654
IAC INVERSE
0.5
0.578
0.375
0.266
0.221
0.196
0.180
0.168
0.160
0.154
0.148
1.0
1.155
0.749
0.532
0.443
0.392
0.360
0.337
0.320
0.307
0.297
2.0
2.310
1.499
1.064
0.885
0.784
0.719
0.674
0.640
0.614
0.594
4.0
4.621
2.997
2.128
1.770
1.569
1.439
1.348
1.280
1.229
1.188
6.0
6.931
4.496
3.192
2.656
2.353
2.158
2.022
1.921
1.843
1.781
8.0
9.242
5.995
4.256
3.541
3.138
2.878
2.695
2.561
2.457
2.375
10.0
11.552
7.494
5.320
4.426
3.922
3.597
3.369
3.201
3.072
2.969
IAC SHORT INVERSE
0.5
0.072
0.047
0.035
0.031
0.028
0.027
0.026
0.026
0.025
0.025
1.0
0.143
0.095
0.070
0.061
0.057
0.054
0.052
0.051
0.050
0.049
2.0
0.286
0.190
0.140
0.123
0.114
0.108
0.105
0.102
0.100
0.099
4.0
0.573
0.379
0.279
0.245
0.228
0.217
0.210
0.204
0.200
0.197
6.0
0.859
0.569
0.419
0.368
0.341
0.325
0.314
0.307
0.301
0.296
8.0
1.145
0.759
0.559
0.490
0.455
0.434
0.419
0.409
0.401
0.394
10.0
1.431
0.948
0.699
0.613
0.569
0.542
0.524
0.511
0.501
0.493
T
TDM
A
B
I I
pkp
⁄
(
)
C
–
------------------------------
D
I I
pkp
⁄
(
)
C
–
(
)
2
--------------------------------------
E
I I
pkp
⁄
(
)
C
–
(
)
3
--------------------------------------
+
+
+
×
=
T
RESET
TDM
t
r
1
I I
pkp
⁄
(
)
2
–
--------------------------------
×
=
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...