5-204
F60 Feeder Protection System
GE Multilin
5.6 GROUPED ELEMENTS
5 SETTINGS
5
d) NEGATIVE SEQUENCE DIRECTIONAL OVERCURRENT
(ANSI 67Q, IEC PDEF/PTOC)
PATH: SETTINGS
GROUPED ELEMENTS
SETTING GROUP 1(6)
NEGATIVE SEQUENCE CURRENT
NEG SEQ DIR OC1(2)
There are two negative-sequence directional overcurrent protection elements available. The element provides both forward
and reverse fault direction indications through its output operands
NEG SEQ DIR OC1 FWD
and
NEG SEQ DIR OC1 REV
,
respectively. The output operand is asserted if the magnitude of the operating current is above a pickup level (overcurrent
unit) and the fault direction is seen as
forward
or
reverse
, respectively (directional unit).
The overcurrent unit of the element essentially responds to the magnitude of a fundamental frequency phasor of either the
negative-sequence or neutral current as per user selection.
A positive-sequence restraint is applied for better performance: a small user-programmable portion of the positive-
sequence current magnitude is subtracted from the negative or zero-sequence current magnitude, respectively, when form-
ing the element operating quantity.
(EQ 5.28)
The positive-sequence restraint allows for more sensitive settings by counterbalancing spurious negative-sequence and
zero-sequence currents resulting from:
•
System unbalances under heavy load conditions.
•
Transformation errors of current transformers (CTs).
•
Fault inception and switch-off transients.
NEG SEQ DIR OC1
NEG SEQ DIR OC1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
NEG SEQ DIR OC1
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
NEG SEQ DIR OC1
OFFSET: 0.00
Ω
Range: 0.00 to 250.00 ohms in steps of 0.01
MESSAGE
NEG SEQ DIR OC1
TYPE: Neg Sequence
Range: Neg Sequence, Zero Sequence
MESSAGE
NEG SEQ DIR OC1 POS-
SEQ RESTRAINT: 0.063
Range: 0.000 to 0.500 in steps of 0.001
MESSAGE
NEG SEQ DIR OC1 FWD
ECA: 75° Lag
Range: 0 to 90° Lag in steps of 1
MESSAGE
NEG SEQ DIR OC1 FWD
LIMIT ANGLE: 90°
Range: 40 to 90° in steps of 1
MESSAGE
NEG SEQ DIR OC1 FWD
PICKUP: 0.050
pu
Range: 0.015 to 30.000 pu in steps of 0.001
MESSAGE
NEG SEQ DIR OC1 REV
LIMIT ANGLE: 90°
Range: 40 to 90° in steps of 1
MESSAGE
NEG SEQ DIR OC1 REV
PICKUP: 0.050
pu
Range: 0.015 to 30.000 pu in steps of 0.001
MESSAGE
NEG SEQ DIR OC1 BLK:
Off
Range: FlexLogic operand
MESSAGE
NEG SEQ DIR OC1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
NEG SEQ DIR OC1
EVENTS: Disabled
Range: Disabled, Enabled
I
op
I_2
K
I_1
×
–
=
or
I
op
3
I_0
K
I_1
×
–
(
)
×
=
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...