5-218
F60 Feeder Protection System
GE Multilin
5.6 GROUPED ELEMENTS
5 SETTINGS
5
The undervoltage elements can be programmed to have a definite time delay characteristic. The definite time curve oper-
ates when the voltage drops below the pickup level for a specified period of time. The time delay is adjustable from 0 to
600.00 seconds in steps of 0.01. The undervoltage elements can also be programmed to have an inverse time delay char-
acteristic.
The undervoltage delay setting defines the family of curves shown below.
(EQ 5.29)
where:
T
= operating time
D
= undervoltage delay setting (
D
= 0.00 operates instantaneously)
V
= secondary voltage applied to the relay
V
pickup
= pickup level
Figure 5–95: INVERSE TIME UNDERVOLTAGE CURVES
At 0% of pickup, the operating time equals the UNDERVOLTAGE DELAY setting.
T
D
1
V
V
pickup
------------------
–
----------------------------------
=
842788A1.CDR
% of voltage pickup
T
ime
(seconds)
NOTE
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...