GE Multilin
F60 Feeder Protection System
5-277
5 SETTINGS
5.7 CONTROL ELEMENTS
5
Figure 5–130: INCIPIENT CABLE FAULT DETECTOR SCHEME LOGIC
g) VT FUSE FAILURE
PATH: SETTINGS
CONTROL ELEMENTS
MONITORING ELEMENTS
VT FUSE FAILURE 1(4)
Every signal source includes a fuse failure scheme.
The VT fuse failure detector can be used to raise an alarm and/or block elements that may operate incorrectly for a full or
partial loss of AC potential caused by one or more blown fuses. Some elements that might be blocked (via the
BLOCK
input)
are distance, voltage restrained overcurrent, and directional current.
There are two classes of fuse failure that occur:
•
Class A: loss of one or two phases.
•
Class B: loss of all three phases.
Different means of detection are required for each class. An indication of class A failures is a significant level of negative-
sequence voltage, whereas an indication of class B failures is when positive sequence current is present and there is an
insignificant amount of positive sequence voltage. Also rapid decrease in the phase voltages magnitude from a healthy
voltage level without disturbance in current can indicate a VT fuse fail conditions. These noted indications of fuse failure
can also be present when faults are present on the system, so a means of detecting faults and inhibiting fuse failure decla-
rations during these events is provided.
Once the fuse failure condition is declared, it is sealed-in until the cause that generated it disappears.
An additional condition is introduced to inhibit a fuse failure declaration when the monitored circuit is de-energized; positive-
sequence voltage and current are both below threshold levels.
The
VT FUSE FAILURE 1 FUNCTION
setting enables and disables the fuse failure feature for Source 1 VT Fuse Fail.
The
VT NEU WIRE OPEN 1 FUNCTION
setting enables and disables the VT neutral wire open detection function. When the
VT is connected in Delta, do not enabled this function because there is no neutral wire for Delta connected VT.
VT FUSE FAILURE 1
VT FUSE FAILURE 1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
NEUTRAL WIRE OPEN 1
DETECTION: Disabled
Range: Disabled, Enabled
MESSAGE
NEUTRAL WIRE OPEN 1
3 HARM PKP: 0.100
Range: 0.000 to 3.000 pu in steps of 0.001
Detection logic
SETTING
= Enabled
= Disabled
INCIPIENT FAULT 1 FUNCTION
SETTING
= OFF
INCIPIENT FAULT 1 BLOCK
SETTING
= IA
= IB
INCIPIENT FAULT 1 SOURCE
= IC
= IN
AND
SETTING
INCIPIENT FAULT 1
PICKUP
RUN
–
> PICKUP
where
is 2 cycles old
I
mag
´
I
I
mag
mag
´
SETTINGS
INCIPNT FLT 1 DETECT
WINDOW
RUN
INCIPIENT FLT 1 TRIP
COUNTS NUMBER
INCIPNT FLT 1 MODE
T
WINDOW
SETTINGS
INCIPIENT FAULT 1
RESET DELAY
0
T
RST
0
T
RST
0
T
RST
FLEXLOGIC OPERANDS
INCIPNT FLT 1 OP A
INCIPNT FLT 1 OP B
INCIPNT FLT 1 OP C
INCIPNT FLT 1 OP
OR
FLEXLOGIC OPERANDS
INCIPNT FLT 1 PKP A
INCIPNT FLT 1
B
PKP
INCIPNT FLT 1
C
PKP
INCIPNT FLT 1 PKP
OR
ACTUAL VALUES
INCIPIENT FAULT 1 PH B
FAULTS
INCIPIENT FAULT 1 PH A
FAULTS
INCIPIENT FAULT 1 PH C
FAULTS
COMMAND
= Yes
CLEAR INCIPIENT FAULT
COUNTERS
RESET
832028A1.CDR
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...