F60 Feeder Protection System
GE Multilin
5.9 TRANSDUCER INPUTS AND OUTPUTS
5 SETTINGS
5
5.9.2 RTD INPUTS
PATH: SETTINGS
TRANSDUCER I/O
RTD INPUTS
RTD INPUT H1(W8)
Hardware and software is provided to receive signals from external resistance temperature detectors and convert these
signals into a digital format for use as required. These channels are intended to be connected to any of the RTD types in
common use. Specific hardware details are contained in chapter 3.
RTD input channels are arranged in a manner similar to CT and VT channels. The user configures individual channels with
the settings shown here.
The channels are arranged in sub-modules of two channels, numbered from 1 through 8 from top to bottom. On power-up,
the relay will automatically generate configuration settings for every channel, based on the order code, in the same general
manner that is used for CTs and VTs. Each channel is assigned a slot letter followed by the row number, 1 through 8 inclu-
sive, which is used as the channel number. The relay generates an actual value for each available input channel.
Settings are automatically generated for every channel available in the specific relay as shown above for the first channel of
a type 5C transducer module installed in the first available slot.
The function of the channel may be either “Enabled” or “Disabled”. If “Disabled”, there will not be an actual value created for
the channel. An alphanumeric ID is assigned to the channel; this ID will be included in the channel actual values. It is also
used to reference the channel as the input parameter to features designed to measure this type of parameter. Selecting the
type of RTD connected to the channel configures the channel.
Actions based on RTD overtemperature, such as trips or alarms, are done in conjunction with the FlexElements feature. In
FlexElements, the operate level is scaled to a base of 100°C. For example, a trip level of 150°C is achieved by setting the
operate level at 1.5 pu. FlexElement operands are available to FlexLogic for further interlocking or to operate an output
contact directly.
Refer to the following table for reference temperature values for each RTD type.
RTD INPUT H1
RTD INPUT H1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
RTD INPUT H1 ID:
RTD Ip 1
Range: Up to 20 alphanumeric characters
MESSAGE
RTD INPUT H1 TYPE:
100
Ω
Nickel
Range: 100
Ω
Nickel, 10
Ω
Copper, 100
Ω
Platinum,
120
Ω
Nickel
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...