6-8
F60 Feeder Protection System
GE Multilin
6.2 STATUS
6 ACTUAL VALUES
6
6.2.12 FLEX STATES
PATH: ACTUAL VALUES
STATUS
FLEX STATES
There are 256 FlexState
TM
bits available. The second line value indicates the state of the given FlexState bit.
6.2.13 ETHERNET
PATH: ACTUAL VALUES
STATUS
ETHERNET
These values indicate the status of the first, second, and third Ethernet links.
6.2.14 REAL TIME CLOCK SYNCHRONIZING
PATH: ACTUAL VALUES
STATUS
REAL TIME CLOCK SYNCHRONIZING
The
RTC Sync Source
actual value is the time synchronizing source the relay is using at present. Possible sources are:
Port 1 PTP Clock, Port 2 PTP Clock, Port 3 PTP Clock, IRIG-B, SNTP, and None. An actual value displays when the relay
includes the IEEE 1588 software option.
The
Grandmaster ID
is the grandmasterIdentity code being received from the present PTP grandmaster, if any. When the
relay is not using any PTP grandmaster, this actual value is zero. The grandmasterIdentity code is specified by PTP to be
globally unique, so one can always know which clock is grandmaster in a system with multiple grandmaster-capable clocks.
FLEX STATES
PARAM 1:
Off
Off
Range: Off, On
MESSAGE
PARAM 2:
Off
Off
Range: Off, On
↓
MESSAGE
PARAM 256: Off
Off
Range: Off, On
ETHERNET
ETHERNET PRI LINK
STATUS: Fail
Range: Fail, OK
MESSAGE
ETHERNET SEC LINK
STATUS: Fail
Range: Fail, OK
MESSAGE
ETHERNET TRD LINK
STATUS: Fail
Range: Fail, OK
REAL TIME CLOCK
SYNCHRONIZING
RTC Sync Source:
None
Range: See text below
MESSAGE
GrandMaster ID:
0X0000000000000000
Range: Any 8 octet value
MESSAGE
Accuracy:
999,999,999 ns
Range: 0 to 999, 999, 999 ns
MESSAGE
Port 1 PTP State:
NO SIGNAL
Range: Disabled, No Signal, Calibrating, Synch’d (No
Pdelay), Synchronized
MESSAGE
Port 2 PTP State:
NO SIGNAL
Range: Disabled, No Signal, Calibrating, Synch’d (No
Pdelay), Synchronized
MESSAGE
Port 3 PTP State:
NO SIGNAL
Range: Disabled, No Signal, Calibrating, Synch’d (No
Pdelay), Synchronized
MESSAGE
PTP - IRIG-B Delta:
500,000,000 ns
Range: -500,000,000 to +500,000,000 ns
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...