GE Multilin
F60 Feeder Protection System
6-11
6 ACTUAL VALUES
6.2 STATUS
6
These values provide information that may be useful for debugging an EGD network. The EGD signature and packet size
for the fast EGD exchange is displayed.
b) SLOW EXCHANGE
PATH: ACTUAL VALUES
STATUS
EGD PROTOCOL STATUS
PRODUCER STATUS
SLOW EXCHANGE 1(2)
These values provide information that may be useful for debugging an EGD network. The EGD signature and packet size
for the slow EGD exchanges are displayed.
6.2.20 TELEPROTECTION CHANNEL TESTS
PATH: ACTUAL VALUES
STATUS
TELEPROT CH TESTS
The status information for two channels is shown here.
•
CHANNEL 1 STATUS
: This represents the receiver status of each channel. If the value is “OK”, teleprotection is
enabled and data is being received from the remote terminal; If the value is “FAIL”, teleprotection enabled and data is
not being received from the remote terminal. If “n/a”, teleprotection is disabled.
•
CHANNEL 1 LOST PACKETS
: Data is transmitted to the remote terminals in data packets at a rate of two packets per
cycle. The number of lost packets represents data packets lost in transmission; this count can be reset to 0 through the
COMMANDS
CLEAR RECORDS
menu.
•
VALIDITY OF CHANNEL CONFIGURATION
: This value displays the current state of the communications channel
identification check, and hence validity. If a remote relay ID does not match the programmed ID at the local relay, the
“FAIL” message will be displayed. The “N/A” value appears if the local relay ID is set to a default value of “0”, the chan-
nel is failed, or if the teleprotection inputs/outputs are not enabled.
MESSAGE
FAST EXCHANGE 1
DATA LENGTH:
0
SLOW EXCHANGE 1
SLOW EXCHANGE 1
SIGNATURE:
0
MESSAGE
SLOW EXCHANGE 1
DATA LENGTH:
0
TELEPROT CH TESTS
CHANNEL 1
STATUS: n/a
Range: n/a, FAIL, OK
MESSAGE
CHANNEL 1 LOST
PACKETS:
1
Range: 1 to 65535 in steps of 1
MESSAGE
CHANNEL 2
STATUS: n/a
Range: n/a, FAIL, OK
MESSAGE
CHANNEL 2 LOST
PACKETS:
1
Range: 1 to 65535 in steps of 1
MESSAGE
VALIDITY OF CHANNEL
CONFIGURATION: FAIL
Range: n/a, FAIL, OK
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...