GE Multilin
F60 Feeder Protection System
6-27
6 ACTUAL VALUES
6.3 METERING
6
6.3.13 TRANSDUCER INPUTS AND OUTPUTS
PATH: ACTUAL VALUES
METERING
TRANSDUCER I/O DCMA INPUTS
DCMA INPUT xx
Actual values for each dcmA input channel that is enabled are displayed with the top line as the programmed channel ID
and the bottom line as the value followed by the programmed units.
PATH: ACTUAL VALUES
METERING
TRANSDUCER I/O RTD INPUTS
RTD INPUT xx
Actual values for each RTD input channel that is enabled are displayed with the top line as the programmed channel ID and
the bottom line as the value.
DCMA INPUT xx
DCMA INPUT xx
0.000 mA
RTD INPUT xx
RTD INPUT xx
-50 °C
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...