6.4 RECORDS
6 ACTUAL VALUES
6
6.4RECORDS
6.4.1 FAULT REPORTS
PATH: ACTUAL VALUES
RECORDS
FAULT REPORTS
FAULT REPORT 1(15)
The latest 15 fault reports can be stored. The most recent fault location calculation (when applicable) is displayed in this
menu, along with the date and time stamp of the event which triggered the calculation. See the
SETTINGS
PRODUCT
SETUP
FAULT REPORTS
menu for assigning the source and trigger for fault calculations. Refer to the
COMMANDS
CLEAR RECORDS
menu for manual clearing of the fault reports and to the
SETTINGS
PRODUCT SETUP
CLEAR RELAY
RECORDS
menu for automated clearing of the fault reports.
6.4.2 EVENT RECORDS
PATH: ACTUAL VALUES
RECORDS
EVENT RECORDS
The event records menu shows the contextual data associated with up to the last 1024 events, listed in chronological order
from most recent to oldest. If all 1024 event records have been filled, the oldest record will be removed as a new record is
added. Each event record shows the event identifier/sequence number, cause, and date/time stamp associated with the
event trigger. See the
COMMANDS
CLEAR RECORDS
menu for clearing event records.
Only major output operands generate events, not every operand. Elements that assert output per phase, for example, log
operating phase output only without asserting the common three-phase operand event.
NO FAULTS TO REPORT
or
FAULT REPORT 1
FAULT 1
LINE ID: SRC 1
Range: SRC 1, SRC 2
MESSAGE
FAULT 1
DATE:
2000/08/11
Range: YYYY/MM/DD
MESSAGE
FAULT 1
TIME:
00:00:00.000000
Range: HH:MM:SS.ssssss
MESSAGE
FAULT 1
TYPE:
ABG
Range: not available if the source VTs are in the “Delta”
configuration
MESSAGE
FAULT 1
LOCATION
00.0 km
Range: not available if the source VTs are in the “Delta”
configuration
MESSAGE
FAULT 1
RECLOSE
SHOT: 0
Range: where applicable
EVENT RECORDS
EVENT: XXXX
RESET OP(PUSHBUTTON)
↓
MESSAGE
EVENT: 3
POWER ON
EVENT 3
DATE: 2000/07/14
MESSAGE
EVENT: 2
POWER OFF
EVENT 3
TIME: 14:53:00.03405
MESSAGE
EVENT: 1
EVENTS CLEARED
Date and Time Stamps
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...