GE Multilin
F60 Feeder Protection System
7-7
7 COMMANDS AND TARGETS
7.1 COMMANDS
7
•
A
RELAY OUT OF SERVICE
event is recorded.
b) MAJOR SELF-TEST ERROR MESSAGES
The major self-test errors are outlined in this section.
•
Latched target message
: Yes.
•
Description of problem
: One or more installed hardware modules is not compatible with the F60 order code.
•
How often the test is performed
: Module dependent.
•
What to do
: Contact the factory and supply the failure code noted in the display. The “xxx” text identifies the failed mod-
ule (for example, F8L).
•
Latched target message
: No.
•
Description of problem
: The configuration of modules does not match the order code stored in the F60.
•
How often the test is performed
: On power up. Afterwards, the backplane is checked for missing cards every five sec-
onds.
•
What to do
: Check all modules against the order code, ensure they are inserted properly, and cycle control power. If
the problem persists, contact the factory.
•
Latched target message
: No.
•
Description of problem
: A FlexLogic equation is incorrect.
•
How often the test is performed
: The test is event driven, performed whenever FlexLogic equations are modified
.
•
What to do
: Finish all equation editing and use self tests to debug any errors.
•
Latched target message
: No.
•
Description of problem
: The
PRODUCT SETUP
INSTALLATION
RELAY SETTINGS
setting indicates the F60 is not pro-
grammed.
•
How often the test is performed
: On power up and whenever the
PRODUCT SETUP
INSTALLATION
RELAY SETTINGS
setting is altered
.
•
What to do
: Program all settings and then set
PRODUCT SETUP
INSTALLATION
RELAY SETTINGS
to “Programmed”
•
Latched target message
: Yes.
•
Description of problem
: Module hardware failure detected. Module Failures 1 to 11 are major. The system can reboot
for four of these, as follows.
MODULE FAILURE 06 — Event message reads SYSTEM INTEGRITRY RECOVERY 06 when a reboot was required
and otherwise MODULE FAILURE 06 when a failure was detected
INCOMPATIBLE H/W:
Contact Factory (xxx)
EQUIPMENT MISMATCH:
with 2nd line detail
FLEXLOGIC ERROR:
with 2nd line detail
UNIT NOT PROGRAMMED:
Check Settings
MODULE FAILURE___:
Contact Factory (xxx)
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...