GE Multilin
F60 Feeder Protection System
2-21
2 PRODUCT DESCRIPTION
2.4 SPECIFICATIONS
2
PHASE OVERVOLTAGE
Voltage:
Phasor only
Pickup level:
0.000 to 3.000 pu in steps of 0.001
Dropout level:
97 to 98% of pickup
Level accuracy:
±0.5% of reading from 10 to 208 V
Pickup delay:
0.00 to 600.00 in steps of 0.01 s
Operate time:
<
30 ms at 1.10
×
pickup at 60 Hz
Timer accuracy:
±3% of operate time or ±1/4 cycle
(whichever is greater)
NEUTRAL OVERVOLTAGE
Pickup level:
0.000 to 3.000 pu in steps of 0.001
Dropout level:
97 to 98% of pickup
Level accuracy:
±0.5% of reading from 10 to 208 V
Pickup delay:
0.00 to 600.00 s in steps of 0.01 (definite
time) or user-defined curve
Reset delay:
0.00 to 600.00 s in steps of 0.01
Curve timing accuracy
at >1.1 x pickup:
±3.5% of operate time or ±1 cycle
(whichever is greater) from pickup to
operate
Operate time:
<
30 ms at 1.10
×
pickup at 60 Hz
AUXILIARY OVERVOLTAGE
Pickup level:
0.000 to 3.000 pu in steps of 0.001
Dropout level:
97 to 98% of pickup
Level accuracy:
±0.5% of reading from 10 to 208 V
Pickup delay:
0 to 600.00 s in steps of 0.01
Reset delay:
0 to 600.00 s in steps of 0.01
Timer accuracy:
±3% of operate time or ±1/4 cycle
(whichever is greater)
Operate time:
<
30 ms at 1.10
×
pickup at 60 Hz
NEGATIVE SEQUENCE OVERVOLTAGE
Pickup level:
0.000 to 1.250 pu in steps of 0.001
Dropout level:
97 to 98% of pickup
Level accuracy:
±0.5% of reading from 10 to 208 V
Pickup delay:
0 to 600.00 s in steps of 0.01
Reset delay:
0 to 600.00 s in steps of 0.01
Timer accuracy:
±3% of operate time or ±20 ms, which-
ever is greater
Operate time:
<30 ms at 1.10
×
pickup at 60 Hz
UNDERFREQUENCY
Minimum signal:
0.10 to 1.25 pu in steps of 0.01
Pickup level:
20.00 to 65.00 Hz in steps of 0.01
Dropout level:
0.03 Hz
Level accuracy:
±0.001 Hz
Time delay:
0 to 65.535 s in steps of 0.001
Timer accuracy:
±3% of operate time or ±1/4 cycle
(whichever is greater)
Operate time:
typically 4 cycles at 0.1 Hz/s change
typically 3.5 cycles at 0.3 Hz/s change
typically 3 cycles at 0.5 Hz/s change
Typical times are average operate times including variables such
as frequency change instance, test method, etc., and may vary by
±0.5 cycles.
OVERFREQUENCY
Pickup level:
20.00 to 65.00 Hz in steps of 0.01
Dropout level:
pickup – 0.03 Hz
Level accuracy:
±0.001 Hz
Time delay:
0 to 65.535 s in steps of 0.001
Timer accuracy:
±3% of operate time or ±1/4 cycle
(whichever is greater)
Operate time:
typically 4 cycles at 0.1 Hz/s change
typically 3.5 cycles at 0.3 Hz/s change
typically 3 cycles at 0.5 Hz/s change
Typical times are average operate times including variables such
as frequency change instance, test method, etc., and may vary by
±0.5 cycles.
RATE OF CHANGE OF FREQUENCY
df/dt trend:
increasing, decreasing, bi-directional
df/dt pickup level:
0.10 to 15.00 Hz/s in steps of 0.01
df/dt dropout level:
96% of pickup
df/dt level accuracy:
80 mHz/s or 3.5%, whichever is greater
Overvoltage supv.:
0.100 to 3.000 pu in steps of 0.001
Overcurrent supv.:
0.000 to 30.000 pu in steps of 0.001
Pickup delay:
0 to 65.535 s in steps of 0.001
Reset delay:
0 to 65.535 s in steps of 0.001
Timer accuracy:
±3% of operate time or ±1/4 cycle
(whichever is greater)
95% settling time for df/dt: <24 cycles
Operate time:
typically 9.5 cycles at 2
×
pickup
typically 8.5 cycles at 3
×
pickup
typically 6.5 cycles at 5
×
pickup
Typical times are average operate times including variables such
as frequency change instance, test method, etc., and may vary by
±0.5 cycles.
BREAKER FAILURE
Mode:
1-pole, 3-pole
Current supervision:
phase, neutral current
Current supv. pickup:
0.001 to 30.000 pu in steps of 0.001
Current supv. dropout:
97 to 98% of pickup
Current supv. accuracy:
0.1 to 2.0
×
CT rating: ±0.75% of reading or ±2% of rated
(whichever is greater)
above 2
×
CT rating:
±2.5% of reading
BREAKER ARCING CURRENT
Principle:
accumulates breaker duty (I
2
t) and mea-
sures fault duration
Initiation:
programmable per phase from any Flex-
Logic operand
Compensation for auxiliary relays: 0 to 65.535 s in steps of 0.001
Alarm threshold:
0 to 50000 kA
2
-cycle in steps of 1
Fault duration accuracy: 0.25 of a power cycle
Availability:
1 per CT bank with a minimum of 2
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...