2-22
F60 Feeder Protection System
GE Multilin
2.4 SPECIFICATIONS
2 PRODUCT DESCRIPTION
2
BREAKER FLASHOVER
Operating quantity:
phase current, voltage and voltage differ-
ence
Pickup level voltage:
0 to 1.500 pu in steps of 0.001
Dropout level voltage:
97 to 98% of pickup
Pickup level current:
0 to 1.500 pu in steps of 0.001
Dropout level current:
97 to 98% of pickup
Level accuracy:
±0.5% or ±0.1% of rated, whichever is
greater
Pickup delay:
0 to 65.535 s in steps of 0.001
Timer accuracy:
±3% of operate time or ±42 ms, which-
ever is greater
Operate time:
<42 ms at 1.10
×
pickup at 60 Hz
BREAKER RESTRIKE
Principle:
detection of high-frequency overcurrent
condition ¼ cycle after breaker opens
Availability:
one per CT/VT module (not including 8Z
modules)
Pickup level:
0.1 to 2.00 pu in steps of 0.01
Reset delay:
0.000 to 65.535 s in steps of 0.001
INCIPIENT CABLE FAULT DETECTION
Principle:
detection of ½ cycle or less overcurrent
condition during normal load
Availability:
two per CT/VT module (not including 8Z
modules)
Pickup level:
0.1 to 10.00 pu in steps of 0.01
Reset delay:
0.000 to 65.535 s in steps of 0.001
Operating mode:
number of counts, counts per time win-
dow
SYNCHROCHECK
Max voltage difference: 0 to 400000 V in steps of 1
Max angle difference:
0 to 100
°
in steps of 1
Max freq. difference:
0.00 to 2.00 Hz in steps of 0.01
Hysteresis for max. freq. diff.: 0.00 to 0.10 Hz in steps of 0.01
Dead source function:
None, LV1 & DV2, DV1 & LV2, DV1 or
DV2, DV1 xor DV2, DV1 & DV2
(L = Live, D = Dead)
AUTORECLOSURE
Single breaker applications, 3-pole tripping schemes
Up to 4 reclose attempts before lockout
Independent dead time setting before each shot
Possibility of changing protection settings after each shot with
FlexLogic
LOAD ENCROACHMENT
Responds to:
Positive-sequence quantities
Minimum voltage:
0.000 to 3.000 pu in steps of 0.001
Reach (sec.
Ω
):
0.02 to 250.00
Ω
in steps of 0.01
Impedance accuracy:
±5%
Angle:
5 to 50° in steps of 1
Angle accuracy:
±2°
Pickup delay:
0 to 65.535 s in steps of 0.001
Reset delay:
0 to 65.535 s in steps of 0.001
Timer accuracy:
±3% of operate time or ±1/4 cycle
(whichever is greater)
Operate time:
<30 ms at 60 Hz
THERMAL OVERLOAD PROTECTION
Thermal overload curves: IEC 255-8 curve
Base current:
0.20 to 3.00 pu in steps of 0.01
Overload (
k
) factor:
1.00 to 1.20 pu in steps of 0.05
Trip time constant:
0 to 1000 min. in steps of 1
Reset time constant:
0 to 1000 min. in steps of 1
Minimum reset time:
0 to 1000 min. in steps of 1
Timer accuracy (cold curve): ±100 ms or 2%, whichever is greater
Timer accuracy (hot curve): ±500 ms or 2%, whichever is greater
for
I
p
< 0.9 ×
k
×
I
b
and I / (
k
×
I
b
) > 1.1
TRIP BUS (TRIP WITHOUT FLEXLOGIC)
Number of elements:
6
Number of inputs:
16
Operate time:
<2 ms at 60 Hz
Timer accuracy:
±3% or 10 ms, whichever is greater
2.4.2 USER-PROGRAMMABLE ELEMENTS
FLEXLOGIC
Programming language: Reverse Polish Notation with graphical
visualization (keypad programmable)
Lines of code:
512
Internal variables:
64
Supported operations:
NOT, XOR, OR (2 to 16 inputs), AND (2
to 16 inputs), NOR (2 to 16 inputs),
NAND (2 to 16 inputs), latch (reset-domi-
nant), edge detectors, timers
Inputs:
any logical variable, contact, or virtual
input
Number of timers:
32
Pickup delay:
0 to 60000 (ms, sec., min.) in steps of 1
Dropout delay:
0 to 60000 (ms, sec., min.) in steps of 1
FLEXCURVES™
Number:
4 (A through D)
Reset points:
40 (0 through 1 of pickup)
Operate points:
80 (1 through 20 of pickup)
Time delay:
0 to 65535 ms in steps of 1
FLEX STATES
Number:
up to 256 logical variables grouped
under 16 Modbus addresses
Programmability:
any logical variable, contact, or virtual
input
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...