GE Multilin
F60 Feeder Protection System
2-23
2 PRODUCT DESCRIPTION
2.4 SPECIFICATIONS
2
FLEXELEMENTS™
Number of elements:
8
Operating signal:
any analog actual value, or two values in
differential mode
Operating signal mode: signed or absolute value
Operating mode:
level, delta
Comparator direction:
over, under
Pickup Level:
–90.000 to 90.000 pu in steps of 0.001
Hysteresis:
0.1 to 50.0% in steps of 0.1
Delta dt:
20 ms to 60 days
Pickup & dropout delay: 0.000 to 65.535 s in steps of 0.001
NON-VOLATILE LATCHES
Type:
set-dominant or reset-dominant
Number:
16 (individually programmed)
Output:
stored in non-volatile memory
Execution sequence:
as input prior to protection, control, and
FlexLogic
USER-PROGRAMMABLE LEDs
Number:
48 plus trip and alarm
Programmability:
from any logical variable, contact, or vir-
tual input
Reset mode:
self-reset or latched
LED TEST
Initiation:
from any contact input or user-program-
mable condition
Number of tests:
3, interruptible at any time
Duration of full test:
approximately 3 minutes
Test sequence 1:
all LEDs on
Test sequence 2:
all LEDs off, one LED at a time on for 1 s
Test sequence 3:
all LEDs on, one LED at a time off for 1 s
USER-DEFINABLE DISPLAYS
Number of displays:
16
Lines of display:
2
×
20 alphanumeric characters
Parameters:
up to 5, any Modbus register addresses
Invoking and scrolling:
keypad, or any user-programmable con-
dition, including pushbuttons
CONTROL PUSHBUTTONS
Number of pushbuttons: 7
Operation:
drive FlexLogic operands
USER-PROGRAMMABLE PUSHBUTTONS (OPTIONAL)
Number of pushbuttons: 12 on standard front panel
16 on enhanced horizontal front panel
6 on enhanced vertical front panel
Mode:
self-reset, latched
Display message:
2 lines of 20 characters each
Drop-out timer:
0.00 to 60.00 s in steps of 0.05
Autoreset timer:
0.2 to 600.0 s in steps of 0.1
Hold timer:
0.0 to 10.0 s in steps of 0.1
SELECTOR SWITCH
Number of elements:
2
Upper position limit:
1 to 7 in steps of 1
Selecting mode:
time-out or acknowledge
Time-out timer:
3.0 to 60.0 s in steps of 0.1
Control inputs:
step-up and 3-bit
Power-up mode:
restore from non-volatile memory or syn-
chronize to a 3-bit control input or synch/
restore mode
DIGITAL ELEMENTS
Number of elements:
48
Operating signal:
any FlexLogic operand
Pickup delay:
0.000 to 999999.999 s in steps of 0.001
Dropout delay:
0.000 to 999999.999 s in steps of 0.001
Timing accuracy:
±3% or ±4 ms, whichever is greater
2.4.3 MONITORING
OSCILLOGRAPHY
Maximum records:
64
Sampling rate:
64 samples per power cycle
Triggers:
any element pickup, dropout, or operate;
contact input change of state; contact
output change of state; FlexLogic equa-
tion
Data:
AC input channels; element state; con-
tact input state; contact output state
Data storage:
in non-volatile memory
EVENT RECORDER
Capacity:
1024 events
Time-tag:
to 1 microsecond
Triggers:
any element pickup, dropout, or operate;
contact input change of state; contact
output change of state; self-test events
Data storage:
in non-volatile memory
DATA LOGGER
Number of channels:
1 to 16
Parameters:
any available analog actual value
Sampling rate:
15 to 3600000 ms in steps of 1
Trigger:
any FlexLogic operand
Mode:
continuous or triggered
Storage capacity:
(NN is dependent on memory)
1-second rate:
01 channel for NN days
16 channels for NN days
↓
60-minute rate:
01 channel for NN days
16 channels for NN days
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...