2.4 SPECIFICATIONS
2 PRODUCT DESCRIPTION
2
FAULT LOCATOR
Method:
single-ended
Voltage source:
wye-connected VTs, delta-connected
VTs and neutral voltage, delta-connected
VTs and zero-sequence current (approxi-
mation)
Maximum accuracy if:
fault resistance is zero or fault currents
from all line terminals are in phase
Relay accuracy:
±1.5% (V > 10 V, I > 0.1 pu)
Worst-case accuracy:
VT
%error
+
user data
CT
%error
+
user data
Z
Line%error
+
user data
METHOD
%error
+
see chapter 8
RELAY ACCURACY
%error
+ (1.5%)
HI-Z
Detections:
Arc Suspected, Arc Detected, Downed
Conductor, Phase Identification
PHASOR MEASUREMENT UNIT
Output format:
per IEEE C37.118 or IEC 61850-90-5
standard
Number of channels:
14 synchrophasors, 8 analogs, 16 digi-
tals
TVE (total vector error) <1%
Triggering:
frequency, voltage, current, power, rate
of change of frequency, user-defined
Reporting rate:
1, 2, 5, 10, 12, 15, 20, 25, 30, 50, or 60
times per second for P and M class, and
100 or 120 times per second for P class
only
Number of clients:
One over TCP/IP port and one over
UDP/IP per aggregator
AC ranges:
As indicated in appropriate specifications
sections
Network reporting format: 16-bit integer (for IEEE C37.118) or 32-
bit IEEE floating point numbers
Network reporting style: rectangular (real and imaginary for IEEE
C37.188) or polar (magnitude and angle)
coordinates
Post-filtering:
none, 3-point, 5-point, 7-point
Calibration:
±5° (angle) and ±5% (magnitude)
2.4.4 METERING
RMS CURRENT: PHASE, NEUTRAL, AND GROUND
Accuracy at
0.1 to 2.0
×
CT rating: ±0.25% of reading or ±0.1% of rated
(whichever is greater)
>
2.0
×
CT rating:
±1.0% of reading
RMS VOLTAGE
Accuracy:
±0.5% of reading from 10 to 208 V
REAL POWER (WATTS)
Accuracy at 0.1 to 1.5 x
CT rating and 0.8 to
1.2 x VT rating:
±1.0% of reading at –1.0
≤
PF< –0.8 and
0.8 < PF
≤
10
REACTIVE POWER (VARS)
Accuracy at 0.1 to 1.5 x
CT rating and 0.8 to
1.2 x VT rating:
±1.0% of reading at –0.2
≤
PF
≤
0.2
APPARENT POWER (VA)
Accuracy at 0.1 to 1.5 x
CT rating and 0.8 to
1.2 x VT rating:
±1.0% of reading
WATT-HOURS (POSITIVE AND NEGATIVE)
Accuracy:
±2.0% of reading
Range:
±0 to 1
×
10
6
MWh
Parameters:
three-phase only
Update rate:
50 ms
VAR-HOURS (POSITIVE AND NEGATIVE)
Accuracy:
±2.0% of reading
Range:
±0 to 1
×
10
6
Mvarh
Parameters:
three-phase only
Update rate:
50 ms
CURRENT HARMONICS
Harmonics:
2nd to 25th harmonic: per phase, dis-
played as a % of f
1
(
fundamental fre-
quency phasor)
THD: per phase, displayed as a % of f
1
Accuracy:
HARMONICS:
1. f
1
> 0.4pu: (0.20% + 0.035% / harmonic) of
reading or 0.15% of 100%, whichever is
greater
2. f
1
< 0.4pu: as above plus %error of f
1
THD:
1. f
1
> 0.4pu: (0.25% + 0.035% / harmonic) of
reading or 0.20% of 100%, whichever is
greater
2. f
1
< 0.4pu: as above plus %error of f
1
VOLTAGE HARMONICS
Harmonics:
2nd to 25th harmonic: per phase, dis-
played as a % of f
1
(
fundamental fre-
quency phasor)
THD: per phase, displayed as a % of f
1
Accuracy:
HARMONICS:
1. f
1
> 0.4pu: (0.20% + 0.035% / harmonic) of
reading or 0.15% of 100%, whichever is
greater
2. f
1
< 0.4pu: as above plus %error of f
1
THD:
1. f
1
> 0.4pu: (0.25% + 0.035% / harmonic) of
reading or 0.20% of 100%, whichever is
greater
2. f
1
< 0.4pu: as above plus %error of f
1
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...