2 PRODUCT DESCRIPTION
2.4 SPECIFICATIONS
2
FREQUENCY
Accuracy at
V = 0.8 to 1.2 pu:
±0.001 Hz (when voltage signal is used
for frequency measurement)
I = 0.1 to 0.25 pu:
±0.005 Hz
I > 0.25 pu:
±0.02 Hz (when current signal is used for
frequency measurement)
DEMAND
Measurements:
Phases A, B, and C present and maxi-
mum measured currents
3-Phase Power (P, Q, and S) present
and maximum measured currents
Accuracy:
±2.0%
2.4.5 INPUTS
AC CURRENT
CT rated primary:
1 to 50000 A
CT rated secondary:
1 A or 5 A by connection
Relay burden:
< 0.2 VA at rated secondary
Conversion range:
Standard CT:
0.02 to 46
×
CT rating RMS symmetrical
Sensitive Ground CT module:
0.002 to 4.6
×
CT rating RMS symmetrical
HI-Z CT module:
0.002 to 4.6
×
CT rating RMS symmetri-
cal
Current withstand:
20 ms at 250 times rated
1 sec at 100 times rated
continuous 4xInom
Short circuit rating:150000 RMS sym-
metrical amperes, 250 V maximum (pri-
mary current to external CT)
AC VOLTAGE
VT rated secondary:
50.0 to 240.0 V
VT ratio:
1.00 to 24000.00
Relay burden:
< 0.25 VA at 120 V
Conversion range:
1 to 275 V
Voltage withstand:
continuous at 260 V to neutral
1 min/hr at 420 V to neutral
FREQUENCY
Nominal frequency setting:25 to 60 Hz
Sampling frequency:
64 samples per power cycle
Tracking frequency range:20 to 70 Hz
CONTACT INPUTS
Dry contacts:
1000
Ω
maximum
Wet contacts:
300 V DC maximum
Selectable thresholds:
17 V, 33 V, 84 V, 166 V
Tolerance:
±10%
Contacts per common return: 4
Recognition time:
< 1 ms
Debounce time:
0.0 to 16.0 ms in steps of 0.5
Continuous current draw:4 mA (when energized)
CONTACT INPUTS WITH AUTO-BURNISHING
Dry contacts:
1000
Ω
maximum
Wet contacts:
300 V DC maximum
Selectable thresholds:
17 V, 33 V, 84 V, 166 V
Tolerance:
±10%
Contacts per common return: 2
Recognition time:
< 1 ms
Debounce time:
0.0 to 16.0 ms in steps of 0.5
Continuous current draw:4 mA (when energized)
Auto-burnish impulse current: 50 to 70 mA
Duration of auto-burnish impulse: 25 to 50 ms
DCMA INPUTS
Current input (mA DC): 0 to –1, 0 to +1, –1 to +1, 0 to 5, 0 to 10,
0 to 20, 4 to 20 (programmable)
Input impedance:
379
Ω
±10%
Conversion range:
–1 to + 20 mA DC
Accuracy:
±0.2% of full scale
Type:
Passive
RTD INPUTS
Types (3-wire):
100
Ω
Platinum, 100 & 120
Ω
Nickel, 10
Ω
Copper
Sensing current:
5 mA
Range:
–50 to +250°C
Accuracy:
±2°C
Isolation:
36 V pk-pk
IRIG-B INPUT
IRIG formats accepted: B000…B007, B120…B127
IRIG control bits:
IEEE Std C37.118.1-2011
Amplitude modulation:
1 to 10 V pk-pk
DC shift:
TTL–Compatible
Input impedance:
50 k
Ω
Isolation:
2 kV
REMOTE INPUTS (IEC 61850 GSSE/GOOSE)
Input points:
32, configured from 64 incoming bit pairs
Remote devices:
16
Default states on loss of comms.: On, Off, Latest/Off, Latest/On
Remote DPS inputs:
5
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...