B-8
F60 Feeder Protection System
GE Multilin
B.3 FILE TRANSFERS
APPENDIX B
B
e) READING DATA LOGGER FILES
Familiarity with the data logger feature is required to understand this description. Refer to the Data Logger section of Chap-
ter 5 for details. To read the entire data logger in binary COMTRADE format, read the following files.
datalog.cfg
and
datalog.dat
To read the entire data logger in ASCII COMTRADE format, read the following files.
dataloga.cfg
and
dataloga.dat
To limit the range of records to be returned in the COMTRADE files, append the following to the filename before writing it:
•
To read from a specific time to the end of the log: <space> startTime
•
To read a specific range of records: <space> startTime <space> endTime
•
Replace <startTime> and <endTime> with the number of seconds since Jan. 1 1970 as numeric text
f) READING EVENT RECORDER FILES
To read the entire event recorder contents in ASCII format (the only available format), use the following filename:
EVT.TXT
To read from a specific record to the end of the log, use the following filename:
EVTnnn.TXT
(replace
nnn
with the desired starting record number)
To read from a specific record to another specific record, use the following filename:
EVT.TXT xxxxx yyyyy
(replace
xxxxx
with the starting record number and
yyyyy
with the ending record number)
g) READING FAULT REPORT FILES
Fault report data has been available via the F60 file retrieval mechanism since UR firmware version 2.00. The file name is
faultReport#####.htm
. The ##### refers to the fault report record number. The fault report number is a counter that
indicates how many fault reports have ever occurred. The counter rolls over at a value of 65535. Only the last ten fault
reports are available for retrieval; a request for a non-existent fault report file will yield a null file. The current value fault
report counter is available in “Number of Fault Reports” Modbus register at location 0x3020.
For example, if 14 fault reports have occurred then the files
faultReport5.htm
,
faultReport6.htm
, up to
faultReport14.htm
are available to be read. The expected use of this feature has an external master periodically poll-
ing the “Number of Fault Reports' register. If the value changes, then the master reads all the new files.
The contents of the file is in standard HTML notation and can be viewed via any commercial browser.
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...