GE Multilin
F60 Feeder Protection System
2-31
2 PRODUCT DESCRIPTION
2.4 SPECIFICATIONS
2
2.4.11 TYPE TESTS
F60 TYPE TESTS
2.4.12 PRODUCTION TESTS
THERMAL
Products go through an environmental test based upon an
Accepted Quality Level (AQL) sampling process.
TEST
REFERENCE STANDARD
TEST LEVEL
Dielectric voltage withstand
EN 60255-5
2.2 kV
Impulse voltage withstand
EN 60255-5
5 kV
Damped oscillatory
IEC 61000-4-18 / IEC 60255-22-1
2.5 kV CM, 1 kV DM
Electrostatic discharge
EN 61000-4-2 / IEC 60255-22-2
Level 3
RF immunity
EN 61000-4-3 / IEC 60255-22-3
Level 3
Fast transient disturbance
EN 61000-4-4 / IEC 60255-22-4
Class A and B
Surge immunity
EN 61000-4-5 / IEC 60255-22-5
Level 3 and 4
Conducted RF immunity
EN 61000-4-6 / IEC 60255-22-6
Level 3
Power frequency immunity
EN 61000-4-7 / IEC 60255-22-7
Class A and B
Voltage interruption and ripple DC
IEC 60255-11
12% ripple, 200 ms interrupts
Radiated and conducted emissions
CISPR11 / CISPR22 / IEC 60255-25
Class A
Sinusoidal vibration
IEC 60255-21-1
Class 1
Shock and bump
IEC 60255-21-2
Class 1
Seismic
IEC 60255-21-3
Class 1
Power magnetic immunity
IEC 61000-4-8
Level 5
Pulse magnetic immunity
IEC 61000-4-9
Level 4
Damped magnetic immunity
IEC 61000-4-10
Level 4
Voltage dip and interruption
IEC 61000-4-11
0, 40, 70, 80% dips; 250 / 300 cycle interrupts
Damped oscillatory
IEC 61000-4-12
2.5 kV CM, 1 kV DM
Conducted RF immunity, 0 to 150 kHz
IEC 61000-4-16
Level 4
Voltage ripple
IEC 61000-4-17
15% ripple
Ingress protection
IEC 60529
IP20 front, IP10 back
Cold
IEC 60068-2-1
–40°C for 16 hours
Hot
IEC 60068-2-2
85°C for 16 hours
Humidity
IEC 60068-2-30
6 days, variant 1
Damped oscillatory
IEEE/ANSI C37.90.1
2.5 kV, 1 MHz
RF immunity
IEEE/ANSI C37.90.2
20 V/m, 80 MHz to 1 GHz
Safety
UL 508
e83849 NKCR
Safety
UL C22.2-14
e83849 NKCR7
Safety
UL 1053
e83849 NKCR
Safety
IEC 60255-27
Insulation: class 1, Pollution degree: 2, Over
voltage cat II
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...