5-108
F35 Multiple Feeder Protection System
GE Multilin
5.5 GROUPED ELEMENTS
5 SETTINGS
5
b) PHASE TIME OVERCURRENT
(ANSI 51P)
PATH: SETTINGS
ÖØ
GROUPED ELEMENTS
Ö
SETTING GROUP 1(6)
Ö
PHASE CURRENT
Ö
PHASE TOC1(6)
The phase time overcurrent element can provide a desired time-delay operating characteristic versus the applied current or
be used as a simple definite time element. The phase current input quantities may be programmed as fundamental phasor
magnitude or total waveform RMS magnitude as required by the application.
Two methods of resetting operation are available: “Timed” and “Instantaneous” (refer to the Inverse
Time overcurrent
curves characteristic
sub-section earlier for details on curve setup, trip times, and reset operation). When the element is
blocked, the time accumulator will reset according to the reset characteristic. For example, if the element reset characteris-
tic is set to “Instantaneous” and the element is blocked, the time accumulator will be cleared immediately.
The
PHASE TOC1 PICKUP
setting can be dynamically reduced by a voltage restraint feature (when enabled). This is accom-
plished via the multipliers (Mvr) corresponding to the phase-phase voltages of the voltage restraint characteristic curve (see
the figure below); the pickup level is calculated as ‘Mvr’ times the
PHASE TOC1 PICKUP
setting. If the voltage restraint feature
is disabled, the pickup level always remains at the setting value.
PHASE TOC1
PHASE TOC1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
PHASE TOC1 SIGNAL
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4, SRC 5, SRC 6
MESSAGE
PHASE TOC1
INPUT: Phasor
Range: Phasor, RMS
MESSAGE
PHASE TOC1
PICKUP: 1.000
pu
Range: 0.000 to 30.000 pu in steps of 0.001
MESSAGE
PHASE TOC1
CURVE: IEEE Mod Inv
Range: See Overcurrent Curve Types table
MESSAGE
PHASE TOC1
TD MULTIPLIER: 1.00
Range: 0.00 to 600.00 in steps of 0.01
MESSAGE
PHASE TOC1
RESET: Instantaneous
Range: Instantaneous, Timed
MESSAGE
PHASE TOC1 VOLTAGE
RESTRAINT: Disabled
Range: Disabled, Enabled
MESSAGE
PHASE TOC1 BLOCK A:
Off
Range: FlexLogic™ operand
MESSAGE
PHASE TOC1 BLOCK B:
Off
Range: FlexLogic™ operand
MESSAGE
PHASE TOC1 BLOCK C:
Off
Range: FlexLogic™ operand
MESSAGE
PHASE TOC1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
PHASE TOC1
EVENTS: Disabled
Range: Disabled, Enabled
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...