GE Multilin
F35 Multiple Feeder Protection System
B-27
APPENDIX B
B.4 MEMORY MAPPING
B
5D50
...Repeated for Ground Time Overcurrent 6
Ground Instantaneous Overcurrent (Read/Write Grouped Setting) (12 modules)
5E00
Ground Instantaneous Overcurrent 1 Signal Source
0 to 5
---
1
F167
0 (SRC 1)
5E01
Ground Instantaneous Overcurrent 1 Function
0 to 1
---
1
F102
0 (Disabled)
5E02
Ground Instantaneous Overcurrent 1 Pickup
0 to 30
pu
0.001
F001
1000
5E03
Ground Instantaneous Overcurrent 1 Delay
0 to 600
s
0.01
F001
0
5E04
Ground Instantaneous Overcurrent 1 Reset Delay
0 to 600
s
0.01
F001
0
5E05
Ground Instantaneous Overcurrent 1 Block
0 to 65535
---
1
F300
0
5E06
Ground Instantaneous Overcurrent 1 Target
0 to 2
---
1
F109
0 (Self-reset)
5E07
Ground Instantaneous Overcurrent 1 Events
0 to 1
---
1
F102
0 (Disabled)
5E08
Reserved (8 items)
0 to 1
---
1
F001
0
5E10
...Repeated for Ground Instantaneous Overcurrent 2
5E20
...Repeated for Ground Instantaneous Overcurrent 3
5E30
...Repeated for Ground Instantaneous Overcurrent 4
5E40
...Repeated for Ground Instantaneous Overcurrent 5
5E50
...Repeated for Ground Instantaneous Overcurrent 6
5E60
...Repeated for Ground Instantaneous Overcurrent 7
5E70
...Repeated for Ground Instantaneous Overcurrent 8
5E80
...Repeated for Ground Instantaneous Overcurrent 9
5E90
...Repeated for Ground Instantaneous Overcurrent 10
5EA0
...Repeated for Ground Instantaneous Overcurrent 11
5EB0
...Repeated for Ground Instantaneous Overcurrent 12
Incipient cable fault detector actual values (read only)
5EC0
Incipient cable fault detector 1 phase A counter
0 to 65535
---
1
F001
0
5EC1
Incipient cable fault detector 1 phase B counter
0 to 65535
---
1
F001
0
5EC2
Incipient cable fault detector 1 phase C counter
0 to 65535
---
1
F001
0
5EC3
...Repeated for incipient cable fault detector 2
5EC6
...Repeated for incipient cable fault detector 3
5EC9
...Repeated for incipient cable fault detector 4
5ECC
...Repeated for incipient cable fault detector 5
5ECF
...Repeated for incipient cable fault detector 6
Setting Groups (Read/Write Setting)
5F80
Setting Group for Modbus Comms (0 means group 1)
0 to 5
---
1
F001
0
5F81
Setting Groups Block
0 to 65535
---
1
F300
0
5F82
FlexLogic to Activate Groups 2 through 6 (5 items)
0 to 65535
---
1
F300
0
5F89
Setting Group Function
0 to 1
---
1
F102
0 (Disabled)
5F8A
Setting Group Events
0 to 1
---
1
F102
0 (Disabled)
Setting Groups (Read Only)
5F8B
Current Setting Group
0 to 5
---
1
F001
0
Setting Group Names (Read/Write Setting)
5F8C
Setting Group 1 Name
---
---
---
F203
(none)
5F94
Setting Group 2 Name
---
---
---
F203
(none)
5F9C
Setting Group 3 Name
---
---
---
F203
(none)
5FA4
Setting Group 4 Name
---
---
---
F203
(none)
5FAC
Setting Group 5 Name
---
---
---
F203
(none)
5FB4
Setting Group 6 Name
---
---
---
F203
(none)
Autoreclose (Read/Write Setting) (6 modules)
6240
Autoreclose 1 Function
0 to 1
---
1
F102
0 (Disabled)
6241
Autoreclose 1 Initiate
0 to 65535
---
1
F300
0
6242
Autoreclose 1 Block
0 to 65535
---
1
F300
0
6243
Autoreclose 1 Max Number of Shots
1 to 4
---
1
F001
1
6244
Autoreclose 1 Manual Close
0 to 65535
---
1
F300
0
6245
Autoreclose 1 Manual Reset from LO
0 to 65535
---
1
F300
0
6246
Autoreclose 1 Reset Lockout if Breaker Closed
0 to 1
---
1
F108
0 (Off)
Table B–9: MODBUS MEMORY MAP (Sheet 20 of 48)
ADDR
REGISTER NAME
RANGE
UNITS
STEP
FORMAT
DEFAULT
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...