GE Multilin
F35 Multiple Feeder Protection System
2-9
2 PRODUCT DESCRIPTION
2.2 SPECIFICATIONS
2
8-BIT SWITCH
Number of elements:
6
Input signals:
two 8-bit integers via FlexLogic™ oper-
ands
Control signal:
any FlexLogic™ operand
Response time:
< 8 ms at 60 Hz, < 10 ms at 50 Hz
DIGITAL ELEMENTS
Number of elements:
48
Operating signal:
any FlexLogic™ operand
Pickup delay:
0.000 to 999999.999 s in steps of 0.001
Dropout delay:
0.000 to 999999.999 s in steps of 0.001
Timing accuracy:
±3% or ±4 ms, whichever is greater
2.2.3 MONITORING
OSCILLOGRAPHY
Maximum records:
64
Sampling rate:
64 samples per power cycle
Triggers:
any element pickup, dropout, or operate;
digital input change of state; digital out-
put change of state; FlexLogic™ equa-
tion
Data:
AC input channels; element state; digital
input state; digital output state
Data storage:
in non-volatile memory
EVENT RECORDER
Capacity:
1024 events
Time-tag:
to 1 microsecond
Triggers:
any element pickup, dropout, or operate;
digital input change of state; digital out-
put change of state; self-test events
Data storage:
in non-volatile memory
DATA LOGGER
Number of channels:
1 to 16
Parameters:
any available analog actual value
Sampling rate:
15 to 3600000 ms in steps of 1
Trigger:
any FlexLogic™ operand
Mode:
continuous or triggered
Storage capacity:
(NN is dependent on memory)
1-second rate:
01 channel for NN days
16 channels for NN days
↓
60-minute rate:
01 channel for NN days
16 channels for NN days
FAULT LOCATOR
Number of independent fault locators: 1 per CT bank (to a maxi-
mum of 5)
Method:
single-ended
Voltage source:
wye-connected VTs, delta-connected
VTs and neutral voltage, delta-connected
VTs and zero-sequence current (approxi-
mation)
Maximum accuracy if:
fault resistance is zero or fault currents
from all line terminals are in phase
Relay accuracy:
±1.5% (V > 10 V, I > 0.1 pu)
Worst-case accuracy:
VT
%error
+
user data
CT
%error
+
user data
Z
Line%error
+
user data
METHOD
%error
+
see chapter 8
RELAY ACCURACY
%error
+ (1.5%)
2.2.4 METERING
RMS CURRENT: PHASE, NEUTRAL, AND GROUND
Accuracy at
0.1 to 2.0
×
CT rating:
±0.25% of reading or ±0.1% of rated
(whichever is greater)
>
2.0
×
CT rating:
±1.0% of reading
RMS VOLTAGE
Accuracy:
±0.5% of reading from 10 to 208 V
REAL POWER (WATTS)
Accuracy:
±1.0% of reading at
–0.8
<
PF
≤
–1.0 and 0.8
<
PF
≤
1.0
REACTIVE POWER (VARS)
Accuracy:
±1.0% of reading at –0.2
≤
PF
≤
0.2
APPARENT POWER (VA)
Accuracy:
±1.0% of reading
WATT-HOURS (POSITIVE AND NEGATIVE)
Accuracy:
±2.0% of reading
Range:
±0 to 1
×
10
6
MWh
Parameters:
three-phase only
Update rate:
50 ms
VAR-HOURS (POSITIVE AND NEGATIVE)
Accuracy:
±2.0% of reading
Range:
±0 to 1
×
10
6
Mvarh
Parameters:
three-phase only
Update rate:
50 ms
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...