E-8
F35 Multiple Feeder Protection System
GE Multilin
E.2 DNP POINT LISTS
APPENDIX E
E
E.2DNP POINT LISTS
E.2.1 BINARY INPUT POINTS
The DNP binary input data points are configured through the
PRODUCT SETUP
ÖØ
COMMUNICATIONS
ÖØ
DNP / IEC104 POINT
LISTS
Ö
BINARY INPUT / MSP POINTS
menu. Refer to the
Communications
section of Chapter 5 for additional details. When a
freeze function is performed on a binary counter point, the frozen value is available in the corresponding frozen counter
point.
BINARY INPUT POINTS
Static (Steady-State) Object Number:
1
Change Event Object Number:
2
Request Function Codes supported:
1 (read), 22 (assign class)
Static Variation reported when variation 0 requested:
2 (Binary Input with status), Configurable
Change Event Variation reported when variation 0 requested:
2 (Binary Input Change with Time), Configurable
Change Event Scan Rate:
8 times per power system cycle
Change Event Buffer Size:
500
Default Class for All Points:
1