3-46
F35 Multiple Feeder Protection System
GE Multilin
3.4 MANAGED ETHERNET SWITCH MODULES
3 HARDWARE
3
3.4.6 ETHERNET SWITCH SELF-TEST ERRORS
The following table provides details about Ethernet module self-test errors.
Be sure to enable the
ETHERNET SWITCH FAIL
setting in the
PRODUCT SETUP
ÖØ
USER-PROGRAMMABLE SELF-TESTS
menu
and the relevant
PORT 1 EVENTS
through
PORT 6 EVENTS
settings under the
PRODUCT SETUP
ÖØ
COMMUNICATIONS
ÖØ
ETH-
ERNET SWITCH
menu.
Table 3–7: ETHERNET SWITCH SELF-TEST ERRORS
ACTIVATION SETTING (SET
AS ENABLED)
EVENT NAME
EVENT CAUSE
POSSIBLE CAUSES
ETHERNET SWITCH FAIL
ETHERNET MODULE
OFFLINE
No response has been
received from the Ethernet
module after five successive
polling attempts.
• Loss of switch power.
• IP/gateway/subnet.
• Incompatibility between the CPU and
the switch module.
• UR port (port 7) configured incorrectly
or blocked
• Switch IP address assigned to another
device in the same network.
PORT 1 EVENTS to PORT 6
EVENTS
ETHERNET PORT 1
OFFLINE to ETHERNET
PORT 6 OFFLINE
An active Ethernet port has
returned a FAILED status.
• Ethernet connection broken.
• An inactive port’s events have been
enabled.
No setting required; the F35
will read the state of a general
purpose input/output port on
the main CPU upon power-up
and create the error if there is a
conflict between the input/
output state and the order
code.
EQUIPMENT
MISMATCH: Card XXX
Missing
The F35 has not detected the
presence of the Ethernet
switch via the bus board.
The F35 failed to see the switch module
on power-up, because switch won’t
power up or is still powering up. To clear
the fault, cycle power to the F35.
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...