5.2 PRODUCT SETUP
5 SETTINGS
5
Refer to the
Control of setting groups
example in the
Control elements
section of this chapter for group activation.
5.2.12 USER-PROGRAMMABLE SELF TESTS
PATH: SETTINGS
Ö
PRODUCT SETUP
ÖØ
USER-PROGRAMMABLE SELF TESTS
All major self-test alarms are reported automatically with their corresponding FlexLogic™ operands, events, and targets.
Most of the minor alarms can be disabled if desired.
When in the “Disabled” mode, minor alarms will not assert a FlexLogic™ operand, write to the event recorder, or display
target messages. Moreover, they will not trigger the
ANY MINOR ALARM
or
ANY SELF-TEST
messages. When in the “Enabled”
mode, minor alarms continue to function along with other major and minor alarms. Refer to the
Relay self-tests
section in
chapter 7 for additional information on major and minor self-test alarms.
To enable the Ethernet switch failure function, ensure that the
ETHERNET SWITCH FAIL FUNCTION
is “Enabled” in this
menu.
Table 5–3: RECOMMENDED SETTINGS FOR USER-PROGRAMMABLE LEDS
SETTING
PARAMETER
SETTING
PARAMETER
LED 1 operand
SETTING GROUP ACT 1
LED 13 operand
Off
LED 2 operand
SETTING GROUP ACT 2
LED 14 operand
BREAKER 2 OPEN
LED 3 operand
SETTING GROUP ACT 3
LED 15 operand
BREAKER 2 CLOSED
LED 4 operand
SETTING GROUP ACT 4
LED 16 operand
BREAKER 2 TROUBLE
LED 5 operand
SETTING GROUP ACT 5
LED 17 operand
SYNC 1 SYNC OP
LED 6 operand
SETTING GROUP ACT 6
LED 18 operand
SYNC 2 SYNC OP
LED 7 operand
Off
LED 19 operand
Off
LED 8 operand
Off
LED 20 operand
Off
LED 9 operand
BREAKER 1 OPEN
LED 21 operand
AR ENABLED
LED 10 operand
BREAKER 1 CLOSED
LED 22 operand
AR DISABLED
LED 11 operand
BREAKER 1 TROUBLE
LED 23 operand
AR RIP
LED 12 operand
Off
LED 24 operand
AR LO
USER-PROGRAMMABLE
SELF TESTS
DIRECT RING BREAK
FUNCTION: Enabled
Range: Disabled, Enabled. Valid for units equipped with
Direct Input/Output module.
MESSAGE
DIRECT DEVICE OFF
FUNCTION: Enabled
Range: Disabled, Enabled. Valid for units equipped with
Direct Input/Output module.
MESSAGE
REMOTE DEVICE OFF
FUNCTION: Enabled
Range: Disabled, Enabled. Valid for units that contain a
CPU with Ethernet capability.
MESSAGE
PRI. ETHERNET FAIL
FUNCTION: Disabled
Range: Disabled, Enabled. Valid for units that contain a
CPU with a primary fiber port.
MESSAGE
SEC. ETHERNET FAIL
FUNCTION: Disabled
Range: Disabled, Enabled. Valid for units that contain a
CPU with a redundant fiber port.
MESSAGE
BATTERY FAIL
FUNCTION: Enabled
Range: Disabled, Enabled.
MESSAGE
SNTP FAIL
FUNCTION: Enabled
Range: Disabled, Enabled. Valid for units that contain a
CPU with Ethernet capability.
MESSAGE
IRIG-B FAIL
FUNCTION: Enabled
Range: Disabled, Enabled.
MESSAGE
ETHERNET SWITCH FAIL
FUNCTION: Disabled
Range: Disabled, Enabled.
NOTE
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...