5-62
F35 Multiple Feeder Protection System
GE Multilin
5.2 PRODUCT SETUP
5 SETTINGS
5
5.2.18 TELEPROTECTION
PATH: SETTINGS
Ö
PRODUCT SETUP
ÖØ
TELEPROTECTION
Digital teleprotection functionality is designed to transfer protection commands between two or three relays in a secure,
fast, dependable, and deterministic fashion. Possible applications are permissive or blocking pilot schemes and direct
transfer trip (DTT). Teleprotection can be applied over any analog or digital channels and any communications media, such
as direct fiber, copper wires, optical networks, or microwave radio links. A mixture of communication media is possible.
Once teleprotection is enabled and the teleprotection input/outputs are configured, data packets are transmitted continu-
ously every 1/4 cycle (3/8 cycle if using C37.94 modules) from peer-to-peer. Security of communication channel data is
achieved by using CRC-32 on the data packet.
Teleprotection inputs/outputs and direct inputs/outputs are mutually exclusive – as such, they cannot be used simu-
latneously. Once teleprotection inputs and outputs are enabled, direct inputs and outputs are blocked, and
vice
versa
.
•
NUMBER OF TERMINALS
: Specifies whether the teleprotection system operates between two peers or three peers.
•
NUMBER OF CHANNELS
: Specifies how many channels are used. If the
NUMBER OF TERMINALS
is “3” (three-terminal
system), set the
NUMBER OF CHANNELS
to “2”. For a two-terminal system, the
NUMBER OF CHANNELS
can set to “1” or
“2” (redundant channels).
•
LOCAL RELAY ID NUMBER
,
TERMINAL 1 RELAY ID NUMBER
, and
TERMINAL 2 RELAY ID NUMBER
: In installa-
tions that use multiplexers or modems, it is desirable to ensure that the data used by the relays protecting a given line
is from the correct relays. The teleprotection function performs this check by reading the message ID sent by transmit-
ting relays and comparing it to the programmed ID in the receiving relay. This check is also used to block inputs if inad-
vertently set to loopback mode or data is being received from a wrong relay by checking the ID on a received channel.
If an incorrect ID is found on a channel during normal operation, the
TELEPROT CH1 ID FAIL
or
TELEPROT CH2 ID FAIL
FlexLogic™ operand is set, driving the event with the same name and blocking the teleprotection inputs. For commis-
sioning purposes, the result of channel identification is also shown in the
STATUS
ÖØ
CHANNEL TESTS
ÖØ
VALIDITY OF
CHANNEL CONFIGURATION
actual value. The default value of “0” for the
LOCAL RELAY ID NUMBER
indicates that relay ID
is not to be checked. On two- terminals two-channel systems, the same
LOCAL RELAY ID NUMBER
is transmitted over
both channels; as such, only the
TERMINAL 1 ID NUMBER
has to be programmed on the receiving end.
5.2.19 INSTALLATION
PATH: SETTINGS
Ö
PRODUCT SETUP
ÖØ
INSTALLATION
TELEPROTECTION
TELEPROTECTION
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
NUMBER OF TERMINALS:
2
Range: 2, 3
MESSAGE
NUMBER OF COMM
CHANNELS: 1
Range: 1, 2
MESSAGE
LOCAL RELAY ID
NUMBER: 0
Range: 0 to 255 in steps of 1
MESSAGE
TERMINAL 1 RELAY ID
NUMBER: 0
Range: 0 to 255 in steps of 1
MESSAGE
TERMINAL 2 RELAY ID
NUMBER: 0
Range: 0 to 255 in steps of 1
INSTALLATION
RELAY SETTINGS:
Not Programmed
Range: Not Programmed, Programmed
MESSAGE
RELAY NAME:
Relay-1
Range: up to 20 alphanumeric characters
NOTE
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...