GE Multilin
F35 Multiple Feeder Protection System
2-7
2 PRODUCT DESCRIPTION
2.2 SPECIFICATIONS
2
2.2SPECIFICATIONS
SPECIFICATIONS ARE SUBJECT TO CHANGE WITHOUT NOTICE
2.2.1 PROTECTION ELEMENTS
The operating times below include the activation time of a trip rated form-A output contact unless otherwise indi-
cated. FlexLogic™ operands of a given element are 4 ms faster. This should be taken into account when using
FlexLogic™ to interconnect with other protection or control elements of the relay, building FlexLogic™ equations, or
interfacing with other IEDs or power system devices via communications or different output contacts.
PHASE/NEUTRAL/GROUND TOC
Current:
Phasor or RMS
Pickup level:
0.000 to 30.000 pu in steps of 0.001
Dropout level:
97% to 98% of pickup
Level accuracy:
for 0.1 to 2.0
×
CT:
±0.5% of reading or ±0.4% of rated
(whichever is greater)
for > 2.0
×
CT:
±1.5% of reading > 2.0
×
CT rating
Curve shapes:
IEEE Moderately/Very/Extremely
Inverse; IEC (and BS) A/B/C and Short
Inverse; GE IAC Inverse, Short/Very/
Extremely Inverse; I
2
t; FlexCurves™
(programmable); Definite Time (0.01 s
base curve)
Curve multiplier:
Time Dial = 0.00 to 600.00 in steps of
0.01
Reset type:
Instantaneous/Timed (per IEEE)
Timing accuracy:
Operate at > 1.03
×
actual pickup
±3.5% of operate time or ±½ cycle
(whichever is greater)
PHASE/NEUTRAL/GROUND IOC
Pickup level:
0.000 to 30.000 pu in steps of 0.001
Dropout level:
97 to 98% of pickup
Level accuracy:
0.1 to 2.0
×
CT rating:
±0.5% of reading or ±0.4% of rated
(whichever is greater)
> 2.0
×
CT rating
±1.5% of reading
Overreach:
<2%
Pickup delay:
0.00 to 600.00 s in steps of 0.01
Reset delay:
0.00 to 600.00 s in steps of 0.01
Operate time:
<16 ms at 3
×
pickup at 60 Hz
(Phase/Ground IOC)
<20 ms at 3
×
pickup at 60 Hz
(Neutral IOC)
Timing accuracy:
Operate at 1.5
×
pickup
±3% or ±4 ms (whichever is greater)
PHASE UNDERVOLTAGE
Pickup level:
0.000 to 3.000 pu in steps of 0.001
Dropout level:
102 to 103% of pickup
Level accuracy:
±0.5% of reading from 10 to 208 V
Curve shapes:
GE IAV Inverse;
Definite Time (0.1s base curve)
Curve multiplier:
Time dial = 0.00 to 600.00 in steps of
0.01
Timing accuracy:
Operate at < 0.90
×
pickup
±3.5% of operate time or ±4 ms (which-
ever is greater)
AUXILIARY UNDERVOLTAGE
Pickup level:
0.000 to 3.000 pu in steps of 0.001
Dropout level:
102 to 103% of pickup
Level accuracy:
±0.5% of reading from 10 to 208 V
Curve shapes:
GE IAV Inverse, Definite Time
Curve multiplier:
Time Dial = 0 to 600.00 in steps of 0.01
Timing accuracy:
±3% of operate time or ±4 ms
(whichever is greater)
NEUTRAL OVERVOLTAGE
Pickup level:
0.000 to 3.000 pu in steps of 0.001
Dropout level:
97 to 98% of pickup
Level accuracy:
±0.5% of reading from 10 to 208 V
Pickup delay:
0.00 to 600.00 s in steps of 0.01 (definite
time) or user-defined curve
Reset delay:
0.00 to 600.00 s in steps of 0.01
Timing accuracy:
±3% or ±20 ms (whichever is greater)
Operate time:
<
30 ms at 1.10
×
pickup at 60 Hz
AUXILIARY OVERVOLTAGE
Pickup level:
0.000 to 3.000 pu in steps of 0.001
Dropout level:
97 to 98% of pickup
Level accuracy:
±0.5% of reading from 10 to 208 V
Pickup delay:
0 to 600.00 s in steps of 0.01
Reset delay:
0 to 600.00 s in steps of 0.01
Timing accuracy:
±3% of operate time or ±4 ms
(whichever is greater)
Operate time:
<
30 ms at 1.10
×
pickup at 60 Hz
UNDERFREQUENCY
Minimum signal:
0.10 to 1.25 pu in steps of 0.01
Pickup level:
20.00 to 65.00 Hz in steps of 0.01
Dropout level:
0.03 Hz
Level accuracy:
±0.001 Hz
Time delay:
0 to 65.535 s in steps of 0.001
Timer accuracy:
±3% or 4 ms, whichever is greater
Operate time:
typically 4 cycles at 0.1 Hz/s change
typically 3.5 cycles at 0.3 Hz/s change
typically 3 cycles at 0.5 Hz/s change
BREAKER ARCING CURRENT
Principle:
accumulates breaker duty (I
2
t) and mea-
sures fault duration
Initiation:
programmable per phase from any Flex-
Logic™ operand
Compensation for auxiliary relays: 0 to 65.535 s in steps of 0.001
Alarm threshold:
0 to 50000 kA2-cycle in steps of 1
Fault duration accuracy: 0.25 of a power cycle
Availability:
1 per CT bank with a minimum of 2
NOTE
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...