E-4
F35 Multiple Feeder Protection System
GE Multilin
E.1 DEVICE PROFILE DOCUMENT
APPENDIX E
E
E.1.2 IMPLEMENTATION TABLE
The following table identifies the variations, function codes, and qualifiers supported by the F35 in both request messages
and in response messages. For static (non-change-event) objects, requests sent with qualifiers 00, 01, 06, 07, or 08, will be
responded with qualifiers 00 or 01. Static object requests sent with qualifiers 17 or 28 will be responded with qualifiers 17 or
28. For change-event objects, qualifiers 17 or 28 are always responded.
Table E–2: IMPLEMENTATION TABLE (Sheet 1 of 4)
OBJECT
REQUEST
RESPONSE
OBJECT
NO.
VARIATION
NO.
DESCRIPTION
FUNCTION
CODES (DEC)
QUALIFIER
CODES (HEX)
FUNCTION
CODES (DEC)
QUALIFIER
CODES (HEX)
1
0
Binary Input (Variation 0 is used to request
default variation)
1
(read)
22
(assign class)
00, 01
(start-stop)
06
(no range, or all)
07, 08
(limited quantity)
17, 28
(index)
1
Binary Input
1
(read)
22
(assign class)
00, 01
(start-stop)
06
(no range, or all)
07, 08
(limited quantity)
17, 28
(index)
129
(response)
00, 01
(start-stop)
17, 28
(index)
(
see Note 2)
2
Binary Input with Status
1
(read)
22
(assign class)
00, 01
(start-stop)
06
(no range, or all)
07, 08
(limited quantity)
17, 28
(index)
129
(response)
00, 01
(start-stop)
17, 28
(index)
(see Note 2)
2
0
Binary Input Change (Variation 0 is used to
request default variation)
1
(read)
06
(no range, or all)
07, 08
(limited quantity)
1
Binary Input Change without Time
1
(read)
06
(no range, or all)
07, 08
(limited quantity)
129
(response)
130
(unsol. resp.)
17, 28
(index)
2
Binary Input Change with Time
1
(read)
06
(no range, or all)
07, 08
(limited quantity)
129
(response
130
(unsol. resp.)
17, 28
(index)
3
Binary Input Change with Relative Time
1
(read)
06
(no range, or all)
07, 08
(limited quantity)
10
0
Binary Output Status (Variation 0 is used to
request default variation)
1
(read)
00, 01
(start-stop)
06
(no range, or all)
07, 08
(limited quantity)
17, 28
(index)
2
Binary Output Status
1
(read)
00, 01
(start-stop)
06
(no range, or all)
07, 08
(limited quantity)
17, 28
(index)
129
(response)
00, 01
(start-stop)
17, 28
(index)
(see Note 2)
12
1
Control Relay Output Block
3
(select)
4
(operate)
5
(direct op)
6 (
dir. op, noack)
00, 01
(start-stop)
07, 08
(limited quantity)
17, 28
(index)
129
(response)
echo of request
20
0
Binary Counter
(Variation 0 is used to request default
variation)
1
(read)
7
(freeze)
8
(freeze noack)
9
(freeze clear)
10
(frz. cl. noack)
22
(assign class)
00, 01
(start-stop)
06
(no range, or all)
07, 08
(limited quantity)
17, 28
(index)
1
32-Bit Binary Counter
1
(read)
7
(freeze)
8
(freeze noack)
9
(freeze clear)
10
(frz. cl. noack)
22
(assign class)
00, 01
(start-stop)
06
(no range, or all)
07, 08
(limited quantity)
17, 28
(index)
129
(response)
00, 01
(start-stop)
17, 28
(index)
(see Note 2)
Note 1:
A default variation refers to the variation responded when variation 0 is requested and/or in class 0, 1, 2, or 3 scans. The default varia-
tions for object types 1, 2, 20, 21, 22, 23, 30, and 32 are selected via relay settings. Refer to the
Communications
section in Chapter 5
for details. This optimizes the class 0 poll data size.
Note 2:
For static (non-change-event) objects, qualifiers 17 or 28 are only responded when a request is sent with qualifiers 17 or 28, respec-
tively. Otherwise, static object requests sent with qualifiers 00, 01, 06, 07, or 08, will be responded with qualifiers 00 or 01 (for change-
event objects, qualifiers 17 or 28 are always responded.)
Note 3:
Cold restarts are implemented the same as warm restarts – the F35 is not restarted, but the DNP process is restarted.
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...