background image

12. Unused pressure alarm switch con-

nections must be plugged.

13. The Pressure Relief Valve provided

with the Dry Pilot Actuation Trim is
factory set to relieve at a pressure of
approximately 45 psi (3,1 bar),
which can typically be used for a
maximum normal dry pilot actuation
system pressure of 40 psi (2,8 bar).
The Pressure Relief Valve may be
reset; however, it must be be reset to
relieve at a pressure which is in ac-
cordance with the requirements of
the authority having jurisdiction.

To reset the Pressure Relief Valve,
first loosen the jam nut and then
adjust the cap accordingly — clock-
wise for a higher pressure setting or
counterclockwise for a lower pres-
sure setting. After verifying the de-
sired pressure setting, tighten the
jam nut.

14. Conduit and electrical connections

are to be made in accordance with
the requirements of the authority
having jurisdiction and/or the Na-
tional Electric Code.

VALVE SETTING PROCEDURE

Steps 1 through 12 are to be per-
formed when initially setting the Model
F470 Multimatic Deluge Valve; after an
operational test of the fire protection
system; or, after system operation due
to a fire.

1. Close the Diaphragm Chamber Sup-

ply Control Valve.

2. Close the Main Control Valve, and if

the system is equipped with Dry Pilot
Actuation, close the Air Supply Con-
trol Valve (Ref. Figure F).

3. Open the Main Drain Valve and all

auxiliary drains in the system. Close
the auxiliary drain valves after water
ceases to discharge. Leave the Main
Drain Valve open.

4. Depress the plunger of the Automat-

ic Drain Valve to verify that it is open
and that the F470 Valve is com-
pletely drained.

5. Push the Reset Knob inward to allow

the Clapper to reseat.

Under normal circumstances, the
reseating of the Clapper can be
heard; however, during an annual
operation test procedure, for exam-
ple, due to minimal flow through a
partially opened main control valve,
the Clapper may not latch open as
shown in Figure C-3. In which case

the reseating sound of the Clapper
will not be heard.

Also under normal circumstances,
water pressure in the riser will have
exerted sufficient force on the Dia-
phragm so as to have emptied most
of the water from the Diaphragm
Chamber which, in turn, will ease
the pushing of the Reset Knob by
eliminating the resistive force pro-
duced by a water filled Diaphragm
Chamber. Therefore, should water
remain in the Diaphragm Chamber,
the Reset Plunger will need to be
depressed with added force to push
the remaining water out of the Dia-
phragm Chamber and through an
open actuation device (e.g., a Dry
Pilot Actuator or Solenoid Valve).

NOTE

If the Reset Knob can not be de-
pressed sufficiently to allow the
Clapper to reseat, operate (open)
the Manual Control Station and
then once again push the Reset
Knob with sufficient force to push
the water out of the Diaphragm
Chamber through the Manual
Control Station drain.

6. Clean the Strainer in the Diaphragm

Chamber Supply connection by re-
moving the clean-out plug and
strainer basket. The Strainer may be
flushed out by momentarily opening
the Diaphragm Chamber Supply
Control Valve.

7. Open the Alarm Control Valve (Fig.

F), if it was closed to silence local
alarms.

It is recommended that the Alarm
Control Valve be wire sealed in the
open position with a No. 16 twisted
wire, the ends of which are secured
by a lead seal. The wire seal should
be looped through the hole in the
handle and tightly twisted around the
pipe nipple adjacent to the handle.

8. Reset the actuation system.

Manual Actuation — Push the oper-
ating lever up; however, do not close
the hinged cover at this time.

Wet Pilot Actuation — Replace op-
erated pilot sprinklers and/or reset
the manual control stations.

Dry Pilot Actuation — Replace oper-
ated pilot sprinklers and/or reset the
manual control stations. Re-estab-
lish dry pilot pneumatic pressure.

Electric Actuation — Reset the elec-
tric detection system in accordance
with the manufacturer’s instructions
to de-energize the solenoid valve.

NOTE

In order to prevent the possibility

of a subsequent operation of an
overheated solder type pilot sprin-
kler, any solder type pilot sprin-
klers which were possibly exposed
to a temperature greater than
their maximum rated ambient
must be replaced.

9. Open the Diaphragm Chamber Sup-

ply Control Valve and allow time for
full pressure to build up in the Dia-
phragm Chamber.

10. Operate (open) the Manual Control

Station to vent trapped air from the
Diaphragm Chamber. If necessary,
first open the hinged cover, and then
fully pull down on the operating lever.
SLOWLY close the operating lever,
by pushing it up, after aerated water
ceases to discharge from the Man-
ual Control Station drain tubing.
Close the hinged cover and insert a
new break rod in the small hole
through the top of the enclosing
box.

If wet pilot actuation is being used,
crack open the Inspector’s Test Con-
nection and any other vent valves, to
relieve trapped air. After the dis-
charge of air has stopped, close the
vent valves and the Inspector’s Test
Connection.

11. Inspect drain connections from the

Manual Control Station, Solenoid
Valve, Dry Pilot Actuator, and Alarm
Devices, as applicable. Any leaks
must be corrected before proceed-
ing to the next step.

12. Slowly open the Main Control Valve.

Close the Main Drain Valve as soon
as water discharges from the drain
connection. Observe the Automatic
Drain Valve for leaks. If there are
leaks, determine/correct the cause
of the leakage problem. If there are
no leaks, the F470 Valve is ready to
be placed in service and the Main
Control Ave must then be fully
opened.

NOTE

After setting a fire protection system,
notify the proper authorities and ad-
vise those responsible for monitoring
proprietary and/or central station
alarms.

-9-

OBSOLETE

Summary of Contents for F470

Page 1: ...rgency manual release of the F470 Valves APPROVALS AND STANDARDS The 4 and 6 inch 100 and 150 mm Model F470 External Resetting Multi matic Deluge Valves are listed by Un derwriters Laboratories Inc and Un derwriters Laboratories of Canada The F470 Valves are also approved by Factory Mutual Research Corporation and the Scientific Services Laborato ries Australia The Model F470 Deluge Valves with ei...

Page 2: ...Pin 22 Handhole Cover 23 Handhole Cover Gasket 24 Handhole Cover Bolt 1 2 13 UNC x 1 1 2 4 req d for 4 valve 3 4 11 UNC x 1 1 2 5 req d for 6 valve Lubricated with Dow Corning FS3452 Flurosilicone Grease Nominal Dimensions in Inches and MM AS 2129 TABLE E ISO 2084 PN10 JIS B 2210 10K 4 100 mm Valve Size 6 150 mm Valve Size A B A B 7 50 190 5 7 00 178 0 7 09 180 0 6 89 175 0 0 75 19 0 0 71 18 0 0 7...

Page 3: ...ted red and the year of manufacture is indicated on the Handhole Cover Components of the F470 Valve are shown in Figure B The Body Hand hole Cover and Diaphragm Cover are ductile iron per ASTM A536 UNS F33100 The Handhole Cover Gasket is neoprene and the Clapper Facing Diaphragm and O Rings are EPDM The Seat Ring Clapper Diaphragm Retainer and the Flange of the Flange Push Rod Assembly are bronze ...

Page 4: ... mm Schedule 40 steel pipe The pilot line is connected to the Wet Pilot Detection connection shown in Figure F 1 Nominal installation dimensions for the Wet Pilot Actuation Trim are shown in Figure D Wet pilot sprinklers are to be minimum 1 2 inch 15 mm orifice listed or ap proved automatic sprinklers Manual Control Stations are to be either the Model F180 or F184 described in Tech nical Data Shee...

Page 5: ...ical Data Sheet TD113 NOTES The dew point of the pilot line air pressure must be maintained below the lowest ambient temperature to which the dry pilot actuation system will be exposed Accumulation of water in the pilot line connection to the Actuator will lower the air pres sure at which the Actuator will open and possibly prevent proper opera tion Also introduction of moisture into the pilot lin...

Page 6: ...ce for example the solenoid valve in the Electric Actuation Trim Ref Fig G 3 releases water from the Diaphragm Chamber faster than it can be replenished through the 1 8 inch 3 2mm Restriction in the Diaphragm Chamber Supply Connection This re sults in a rapid pressure drop in the Diaphragm Chamber and the force dif ferential applied through the Clapper Latch to hold the Clapper down in the set pos...

Page 7: ...orque Size Size Ft Lbs Nm 4 5 8 M16 40 50 54 68 6 3 4 M20 50 65 68 81 1b All nipples fittings and devices must be clean and free of scale and burrs before installation Use pipe thread sealant sparingly on male pipe threads only NOTE It is recommended that internally galvanized pipe and cast iron fit tings be used for wet or dry pilot lines 2 The F470 Valve must be trimmed in accordance with Figure...

Page 8: ...nstalled between a drip leg and the Air Main tenance Device 11 The Low Pressure Alarm Switch for Dry Pilot Actuation is to be adjusted as follows Low pressure alarm setting at approximately 6 psi 0 4 bar below the minimum pilot line service pressure requirement shown in Graph C Fire alarm setting at approxi mately 15 psi 1 0 bar below the minimum pilot line service pressure requirement shown in Gr...

Page 9: ...ficient force to push the water out of the Diaphragm Chamber through the Manual Control Station drain 6 Clean the Strainer in the Diaphragm Chamber Supply connection by re moving the clean out plug and strainer basket The Strainer may be flushed out by momentarily opening the Diaphragm Chamber Supply Control Valve 7 Open the Alarm Control Valve Fig F if it was closed to silence local alarms It is ...

Page 10: ... 10 FIGURE F 1 EXPLODED VIEW OF VALVE TRIM NOTE Refer to Page11 for the corresponding bills of materials O B S O L E T E ...

Page 11: ...re threaded per ANSI B1 20 1 The fit tings are either malleable iron per ANSI B16 3 or cast iron per ANSI B16 4 Standard order trim is provided with black nipples and fittings how ever galvanized nipples and fittings are available on special order 1 300 lb Water Pres sure Gauge 2 req d 2 1 4 Gauge Test Valve 3 Model F180 Manual Control Station 4 2 Angle Valve 5 1 2 Ball Valve 2 req d 6 1 2 Swing C...

Page 12: ...FIGURE G 1 DELUGE VALVE SYSTEM SCHEMATIC WET PILOT ACTUATION FIGURE G 2 DELUGE VALVE SYSTEM SCHEMATIC DRY PILOT ACTUATION 12 O B S O L E T E ...

Page 13: ...est procedure and prior to the F470 Valve being reset the internal parts of the F470 Valve should be cleaned and then inspected for wear and damage Make certain that the two 1 8 inch 3 2mm diameter pressure equalizing vents in the top of the Clapper are open Special consid eration should be given to the condi tion of the Diaphragm and the Clapper Facing The Diaphragm and or Clap per Facing should ...

Page 14: ...ch and drain age of the pilot line condensate should be performed quarterly as follows 1 Close the Diaphragm Chamber Sup ply Control Valve 2 Close the Main Control Valve 3 Open the Main Drain Valve 4 Drain the dry pilot line condensate as follows a Close the Gauge Test Valve lo cated below the Dry Pilot Line Pressure Gauge b Remove the 1 4 Plug from the Gauge Test Valve c Crack Open the Gauge Test...

Page 15: ...1 005 8 O Ring PSN 62 578 1 306 9 Reset Bushing PSN 92 470 1 052 10 O Ring PSN 62 578 1 307 11 Reset Plunger PSN 92 470 1 053 12 Reset Knob PSN 62 470 1 001 13 Diaphragm Cover Bolt PSN 62 039 1 207 14 Diaphragm Retainer PSN 92 470 1 049 15 Flange Push Rod Assembly PSN 92 470 1 040 16 Diaphragm PSN 92 470 1 031 17 Diaphragm Cover PSN 92 470 1 029 20 Clapper Hinge Pin PSN 92 470 1 038 21 Latch Hinge...

Page 16: ... Reg trademark of GRINNELL CORPORATION 3 TYCO PARK EXETER NH 03833 O B S O L E T E ...