F08 Installation & Programming Manual
Document No: LT0082
FIP Installation
2.12
BRIGADE INTERFACE RELAYS
The F08 FIP provides space below the Mains Transformer and Mains Switch for the
installation of the Brigade Interfacing Devices.
A brigade interface bracket is available for fitting the following brigade interfacing units:
(a)
Randata
Deltec
(b)
Mimimux
Deltec
(c)
Tyco Centaur ASE
(d)
Line Isolating Unit; LIU001
(e)
Torrens Transponder Unit
(f)
Transponder Interface Adaptor; TIA001
The F08 provides four (4) sets of voltage free, changeover relay contacts at connector J7, as
shown in Figure 2.17.
The four relays are detailed below.
2.12.1 “STANDBY”
RELAY
(a)
Normally energised coil, (COM closed to NO).
(b)
The Standby Relay de-energises on battery flat voltage, complete battery
power failure, watchdog timeout, or disconnection of the Display/Keyboard flat
ribbon cable. (ie. COM switches from NO to NC).
(c)
THIS RELAY MUST BE USED TO SIGNAL TO THE BRIGADE ON ANY OF
THE ABOVE CONDITIONS, unless otherwise notified by the local Fire
Authority.
(c)
If no "STANDBY" signal is required by the local Fire Authority, it is
recommended that a "LOCAL FAULT" alarm be activated by the "STANDBY"
relay.
** REMEMBER:
WHEN THE "STANDBY" RELAY DE-ENERGISES, THE SYSTEM IS
INDICATING THAT IT IS NO LONGER AN OPERATIONAL FIRE
ALARM PANEL.
2.12.2 “FAULT”
RELAY
(a)
Normally
de-energised.
(b)
The Fault Relay will energise on any non-isolated fault condition on a zone
mapped to the "MASTER ALARM" or the supervised Ancillary Output. ( COM
switches from NC to NO). It will also energise on all enabled zones being
isolated.
Page 2-30
24 March 2006
Issue 3.04