VIGILANT F08 Installation & Programming Manual
Document: LT0082
Programming
4.1
PROGRAMMING
FEATURES
The F08 FIP provides a "PROGRAMMING MODE" so that the installer can configure the
panel to meet specified input and output requirements.
Programming should only be carried out by a suitably qualified FIRE-PROTECTION
technician or engineer.
If the F08 FIP was pre-programmed prior to delivery, it may
NOT NEED TO BE RE-
PROGRAMMED
in the field.
The F08 "PROGRAMMING MODE" provides four (4) programming functions with
the programming keys and indications summarised in Tables 4.1 and 4.2.
FUNCTION 1; ZONE OUTPUT MAPPING
This programming function allows the programmer to select which of the zone inputs will
operate each of the following outputs:
i. Ancillary
Relay
ii. Master
Alarm
iii. Alarm
Bells.
FUNCTION 2; ZONE LATCHING / NON-LATCHING
This programming function enables the programmer to select zone inputs as alarm state
latching or non latching and fault state latching or non-latching.
FUNCTION 3; ZONE INPUT TYPE
This programming function enables the programmer to select for each zone, one of the
following input types. (Refer Section 2.7.2 for a full description):
i.
2 second transient suppression delay to alarm (default). Both detectors and 15V
MCP allowed on circuit.
ii.
AVF/RAD 16 second delay to alarm for detectors, 2 second delay to alarm for 15V
MCP.
iii.
AS1668 SAD. Delay into alarm 2 seconds. Delay out of alarm 60 seconds.
Detector is non-latching and zone should be programmed as non-latching.
iv.
AS1668 AVF/SAD. 16 second AVF delay into alarm. Delay out of alarm 60
seconds. Detector is non-latching and zone should be programmed as non-latching.
v.
Flowswitch. 20 second delay into alarm. No delay out.
vi.
2 second delay to alarm. Detectors only. MCP not allowed. 13-17V band indicates
fault. This circuit type is used to provide line leakage fault indication.
vii.
AVF/RAD 16 second delay into alarm. Detectors only - MCP not allowed. 13-17V
band indicates fault. This circuit type is used to provide line leakage fault indication.
viii.
Fast alarm - 0.5 seconds delay into alarm for supervisory contact with 15V zener
diode. This is typically used for sub-panel monitoring. 0-13V band indicates fault.
ix.
Fast alarm - 500 milliseconds delay into alarm for 0-13V band. 13-17V band is
normal for 15V loop powered circuit.
x.
Delay into alarm is 2 seconds for 13-17V band. 0-13V band is normal for normally
closed (S/C) circuit.
Page 4-2
24 March 2006
Issue 3.04