Document No: LT0082
F08 Installation & Programming Manual
Application
Considerations
5.1.1
FAULT ON STANDBY
Figure 5.1 shows that one AZC of the F08 can be used for monitoring a sub-panel. The
ALARM, FAULT, ISOLATE, and STANDBY relays should be provided in the sub-panel. If
they are not, then they can be left off the wiring.
NOTES:
1)
STANDBY is optional.
2)
STANDBY is normally energised.
3)
SUB-PANEL TO MASTER FIP WIRING MUST BE FIRE RATED
CABLE.
Figure 5.1
Fault on Standby Sub-Panel Circuit Wiring
5.1.2
ALARM ON STANDBY
Figure 5.2 shows how one AZC input of an F08 can be used to monitor a sub-panel with
both alarm and standby from the sub-panel producing alarm at the master panel.
1.
STANDBY is normally energised.
2.
SUB-PANEL TO MASTER FIP MUST BE FIRE RATED CABLE.
Figure 5.2
Alarm on Standby Sub-Panel Circuit Wiring
+
-
EOL
NC
COM
FAULT
NC
COM
ISOLATE
NO
COM
STANDBY
NO
COM
ALARM
F08
AZC
+
-
EOL
NC
COM
FAULT
NC
COM
ISOLATE
NO
COM
STANDBY
F08
AZC
NC
COM
ALARM
Issue 3.04
24 March 2006
Page 5-3