GE Multilin
F35 Multiple Feeder Protection System
5-91
5 SETTINGS
5.4 FLEXLOGIC™
5
5.4.2 FLEXLOGIC™ RULES
When forming a FlexLogic™ equation, the sequence in the linear array of parameters must follow these general rules:
1.
Operands must precede the operator which uses the operands as inputs.
2.
Operators have only one output. The output of an operator must be used to create a virtual output if it is to be used as
an input to two or more operators.
3.
Assigning the output of an operator to a virtual output terminates the equation.
4.
A timer operator (for example, "TIMER 1") or virtual output assignment (for example, " = Virt Op 1") may only be used
once. If this rule is broken, a syntax error will be declared.
5.4.3 FLEXLOGIC™ EVALUATION
Each equation is evaluated in the order in which the parameters have been entered.
FlexLogic™ provides latches which by definition have a memory action, remaining in the set state after the
set input has been asserted. However, they are volatile; that is, they reset on the re-application of control
power.
When making changes to settings, all FlexLogic™ equations are re-compiled whenever any new setting
value is entered, so all latches are automatically reset. If it is necessary to re-initialize FlexLogic™ during
testing, for example, it is suggested to power the unit down and then back up.
Table 5–9: FLEXLOGIC™ OPERATORS
TYPE
SYNTAX
DESCRIPTION
NOTES
Editor
INSERT
Insert a parameter in an equation list.
DELETE
Delete a parameter from an equation list.
End
END
The first END encountered signifies the last entry in
the list of processed FlexLogic™ parameters.
One-shot
POSITIVE ONE SHOT One shot that responds to a positive going edge.
A ‘one shot’ refers to a single input gate
that generates a pulse in response to an
edge on the input. The output from a ‘one
shot’ is True (positive) for only one pass
through the FlexLogic™ equation. There is
a maximum of 64 ‘one shots’.
NEGATIVE ONE
SHOT
One shot that responds to a negative going edge.
DUAL ONE SHOT
One shot that responds to both the positive and
negative going edges.
Logic
gate
NOT
Logical NOT
Operates on the previous parameter.
OR(2)
↓
OR(16)
2 input OR gate
↓
16 input OR gate
Operates on the 2 previous parameters.
↓
Operates on the 16 previous parameters.
AND(2)
↓
AND(16)
2 input AND gate
↓
16 input AND gate
Operates on the 2 previous parameters.
↓
Operates on the 16 previous parameters.
NOR(2)
↓
NOR(16)
2 input NOR gate
↓
16 input NOR gate
Operates on the 2 previous parameters.
↓
Operates on the 16 previous parameters.
NAND(2)
↓
NAND(16)
2 input NAND gate
↓
16 input NAND gate
Operates on the 2 previous parameters.
↓
Operates on the 16 previous parameters.
XOR(2)
2 input Exclusive OR gate
Operates on the 2 previous parameters.
LATCH (S,R)
Latch (set, reset): reset-dominant
The parameter preceding LATCH(S,R) is
the reset input. The parameter preceding
the reset input is the set input.
Timer
TIMER 1
↓
TIMER 32
Timer set with FlexLogic™ timer 1 settings.
↓
Timer set with FlexLogic™ timer 32 settings.
The timer is started by the preceding
parameter. The output of the timer is
TIMER #.
Assign
virtual
output
= Virt Op 1
↓
= Virt Op 96
Assigns previous FlexLogic™ operand to virtual
output 1.
↓
Assigns previous FlexLogic™ operand to virtual
output 96.
The virtual output is set by the preceding
parameter
NOTE
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...